Thread: Ash dump under home
05-26-2019, 11:22 AM #1
Ash dump under home
Doesn't seem right to have an ash dump under the home in a crawlspace. Just looks like a fire hazard if the door is left open or whatever... Im sure there's nothing for this NFPA or ICC wise..is there?
Similar Threads:Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
05-26-2019, 06:07 PM #2
Re: Ash dump under home
From NFPA 211, 2019 Edition (and it's been there for many years):
7.1.4.5 Cleanout openings and doors shall not be obstructed. Combustible material located or projected beyond the face of the chimney shall be kept a minimum of 18 in. (457 mm) away from the cleanout opening.
7.1.4.6 Cleanout doors shall be permanently marked with a message equivalent to the following:
WARNING: DO NOT OBSTRUCT. KEEP COMBUSTIBLE MATERIAL AT LEAST 18 in. (457 mm) AWAY FROM THIS DOOR.
11.2.8 Ash Dumps. Cleanouts, if provided, shall be accessible and located so that ash removal will not create a hazard to combustible materials.
Warmest Regards,
Bart Ogden, President
Home Safe Hearth & Chimney, Inc.
Wichita, KS
CSIA Master Chimney Sweep
NFI Master Hearth Professional
05-26-2019, 06:22 PM #3
You are the man. much thanks
05-29-2019, 09:11 AM #4
05-29-2019, 10:25 AM #5
And don't forget the plywood above is not installed with its face grain perpendicular to the supports.
05-29-2019, 10:27 AM #6