    Default Service and load side panels in close proximity

    Service disconnect is in panel 4" to left of "load side" panel, bonded to same by conduit with ground wires to bushings at both ends (to the respective panels). Feeders run from 100A breaker at service panel to load side panel. Ground and neutral are not isolated at load side panel.

    When the load side panel is in such close proximity to the service panel, and bonded in this manner, is it still considered a load side panel, or is it now part of the "service equipment" ?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Service and load side panels in close proximity

    Quote Originally Posted by Michael Thomas View Post
    When the load side panel is in such close proximity to the service panel, and bonded in this manner, is it still considered a load side panel, or is it now part of the "service equipment" ?
    It is still "separate".

    The dangers of the problem are now reduced to that conduit, but the load side panel is still "non-service equipment" and the neutral needs to be isolated from ground.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Service and load side panels in close proximity

    Thanks.