Results 1 to 6 of 6

Thread: Cu AL breakers

  1. #1
    dan orourke's Avatar
    dan orourke Guest

    Default Cu AL breakers

    Last edited by dan orourke; 01-02-2008 at 09:23 AM.
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Cu AL breakers

    I don't think it was allowed to use stranded aluminum wire in branch circuits.
    How about it Jerry

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Cu AL breakers

    Thanks Dan, I did not know that.
    And , sorry I implied only Jerry would know.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Cu AL breakers

    From the NEC. (bold is mine)
    - 310.14 Aluminum Conductor Material.
    - - Solid aluminum conductors 8, 10, and 12 AWG shall be made of an AA-8000 series electrical grade aluminum alloy conductor material. Stranded aluminum conductors 8 AWG through 1000 kcmil marked as Type RHH, RHW, XHHW, THW, THHW, THWN, THHN, service-entrance Type SE Style U and SE Style R shall be made of an AA-8000 series electrical grade aluminum alloy conductor material.

    #8 AWG can be either solid or stranded, smaller than #8 AWG is to be solid, and larger than #8 AWG is to be stranded.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Cu AL breakers

    I think the original question was about the rating of the breakers for Al.
    Any breaker used for AL must be rated for AL no matter the size.
    Simpler is usually better. (at least it is easier for me to remember)
    Jim

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Cu AL breakers

    Quote Originally Posted by Jim Luttrall View Post
    I think the original question was about the rating of the breakers for Al.
    Any breaker used for AL must be rated for AL no matter the size.
    Simpler is usually better. (at least it is easier for me to remember)
    Jim

    Yes, that was the original question, I answered the later question.

    The simpler way to remember it is that any *terminal* allowed to be used for 'aluminum' is to be marked for use with aluminum.

    Whether that terminal is on a breaker, terminal bar, device (switch/receptacle outlet), etc.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •