3-2-10 rule revisited
Does the 3 feet above the roof line only apply to wood burning fireplaces, not to gas appliances? I can't find anything in the IRC regarding this.
Similar Threads:
-
04-29-2011, 05:53 PM #2
Re: 3-2-10 rule revisited
chimneys
Keep the fire in the fireplace.
-
04-29-2011, 05:57 PM #3
Re: 3-2-10 rule revisited
Thanks Bob. Does a prefabricated gas fireplace with type B vent count as a chimney? Is it OK to have type B vents 4-6 inches above the roof line?
-
04-29-2011, 07:03 PM #4
Re: 3-2-10 rule revisited
Nope and nope.
B-vent is a *vent*--not a *chimney*.
Refer to the gas codes but they start at 12" above a flat roof then go up based upon roof pitch.
Keep the fire in the fireplace.
-
04-29-2011, 07:43 PM #5
Re: 3-2-10 rule revisited
Thanks again Bob! Here is a picture of the vent I thought was too low. It's about 3 feet from the parapet and well below it but not within 3 feet of the corner. I am not sure I understand why a gas appliance would not back draft when a fireplace would? Any insight?
Bvent.jpg
Last edited by Benjamin Thompson; 04-29-2011 at 09:52 PM.
-
04-30-2011, 04:56 AM #6
Re: 3-2-10 rule revisited
You have a vertical obstruction within 8ft horizontally so the flue gas outlet must extend at least 2 feet above the top of that parapet. The 3 ft rule is to allow sparks from wood burning to cool before they land on a possibly combustible roof deck. The 2/10 is to hopefully extend the vent above any pressure zones created by wind effect over a ridge.
The height of a vent above a roofline would have an effect on backdrafting only if it was wind related in which case it may need to extend a lot more than just the code minimum. Codes do not guarantee performance and can be exceeded.
Keep the fire in the fireplace.
-