Today I inspected a "total rehab" with a new 200 Amp panel with a city inspection sticker on it.
All of the AFCI circuit breakers were 20 Amp, with #14 conductors.
Did this guy just not have any 15 Amp AFCIs in the truck? Why would someone think this was ok?
Similar Threads:"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
01-23-2012, 04:05 PM #2
Re: 20 Amp AFCI overfusing
A clear violation. NEC 240.4(D).
01-23-2012, 04:07 PM #3
Drugs?
"It takes a big man to cry. It takes an even bigger man to laugh at that man". - Jack Handey
01-23-2012, 04:34 PM #4
call the city inspector and ask wtf
cvf
01-24-2012, 07:49 AM #5
disregard
Last edited by Mike Gault; 01-24-2012 at 07:51 AM. Reason: made no sense - referenced 240.4 (G)
We know why you fly: because the bus is too expensive and the railroad has a dress code...
www.atozinspector.com
01-26-2012, 11:46 AM #6
01-26-2012, 11:53 AM #7
01-27-2012, 08:52 AM #8
02-05-2012, 03:04 PM #9
Not to belabor the "knowns", 20 OPD with a 14 AWG conductor, but I am curious as to how you made the determination that these were 14 AWG conductors.
Did you pull the panelboard cover and view the connections on the panelboard? Or do just about all of the conductors going into this panelboard have 14 AWG on the cable sheaths?
02-05-2012, 07:26 PM #10
Based on this being a recent rehab it would not be had to see the gauge of the wiring used with type NM cables due to the color coding of the sheath. Also looking at a conductor you should be able to recognize the size.