Results 1 to 15 of 15
-
11-24-2009, 07:00 PM #1
1994 Home, with solid strand aluminium
I thought this was interesting. This place was built in 94 and this circuit is for the range. At first I thought nothing of it, just thought it was stranded. Upon closer inspection I realized it was solid strand. I thought they stopped using solid strand in the early 80's.
Similar Threads:
-
11-24-2009, 08:43 PM #2
Re: 1994 Home, with solid strand aluminium
I thought so too. It looks like copper to me, though.
Jim Robinson
New Mexico, USA
-
11-25-2009, 07:56 AM #3
Re: 1994 Home, with solid strand aluminium
See it all the time on new construction. Solid strand aluminum to a 220/240 dedicated applicance. Very common around here for range, wall oven, dryer, A/C, hot tub, etc.
Licensing board only cares about single strand 110/120 BRANCH circuits.
"The Code is not a peak to reach but a foundation to build from."
-
11-25-2009, 08:30 AM #4
Re: 1994 Home, with solid strand aluminium
Bruce,
Thanks for the info. It is a first for me. Happy Thanksgiving.
-
11-25-2009, 10:49 AM #5
Re: 1994 Home, with solid strand aluminum
Mathew, The solid strand wiring to look out for is branch circuit wiring 14 and 12 AWG. They haven't had the same problems with the heavier gauge wire as long as it has anti-oxidant paste at connections. I see the solid aluminum for appliances here all the time. Somebody correct me if I'm wrong here.
-
11-25-2009, 11:43 AM #6
-
11-25-2009, 01:31 PM #7
Re: 1994 Home, with solid strand aluminium
What AMP breaker is that for the oven Mathew?
-
11-25-2009, 08:07 PM #8
Re: 1994 Home, with solid strand aluminium
40amp
-
11-26-2009, 08:32 AM #9
Re: 1994 Home, with solid strand aluminum
That would require #8 solid strand aluminum. Which it appears to be. Jim, I am curious what you meant that because the wire is larger than # 10 that would make it stranded. I hate it when people jump all over others on this site but if there is something I'm missing I would like to know.
Thanks!!
-
11-26-2009, 10:49 AM #10
Re: 1994 Home, with solid strand aluminium
If that is a Non-Metallic cable or a SE type cable you will need a minimum of a # 6 for 40 amps,
What is the wiring method for the conductors in question? Conduit , if so what type of conductor insulation? Cable ?
Will need the answers before one can determine the ampacity allowed.
-
11-28-2009, 12:35 PM #11
Re: 1994 Home, with solid strand aluminium
Ken,
I may be misunderstanding the question, but here is what is noticed. The wire in NM sheathed and there was nt conduit. I could see where it came through the back of the wall in the kitchen. For some reason they had an access panel, must have been for installation of a water line to the frig. Is that the info you are looking for.
-
11-29-2009, 10:44 AM #12
Re: 1994 Home, with solid strand aluminium
Yep
If thats NM Cable or SE cable- then it is limited to the 60 degree column in article 310.80 of the NEC.
You say it's on a 40 ampere circuit breaker, then the conductor size should be a #6 minimum.
If it's a #8 NM cable then it can not be on a 40 ampere circuit breaker as # 8 aluminum NM Cable is only rated for 30 amps.
#10 Aluminum = 20 amperes
#12 Aluminum = 15 amperes
-
11-29-2009, 07:12 PM #13
Re: 1994 Home, with solid strand aluminium
Last edited by Rollie Meyers; 11-29-2009 at 07:56 PM.
-
11-29-2009, 07:56 PM #14
Re: 1994 Home, with solid strand aluminium
Thanks
-
11-30-2009, 03:43 PM #15
Bookmarks