Results 1 to 6 of 6

Thread: MINI VENT

  1. #1
    Ron Bibler's Avatar
    Ron Bibler Guest

    Default MINI VENT

    OREP Insurance

  2. #2
    Joseph P. Hagarty's Avatar
    Joseph P. Hagarty Guest

  3. #3
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: MINI VENT

    I see them once in a while, but usually in the attic. I have seen one or two in the sink base cabinets though.

    http://www.studor.com/products/mini-...iSpecSheet.pdf

    http://www.icc-es.org/reports/pdf_files/NES/NER592.pdf

    Under conditions of use in the 2nd document see:

    7.2
    Each Studor Mini-Vent®, Maxi-Vent®, and Tec-Vent™
    shall be located a minimum of 4 inches above the
    weir of the fixture trap when providing trap seal
    protection for fixtures or branches.

    Aaron




  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: MINI VENT

    It looks like that might make the minimum required height, it is also well within the 15 degrees of vertical it is required to be, has adequate space around it to allow for its removal and replacement, however, it is require to have pipe thread tape around its threads and that looks like pipe dope - which is not allowed.

    You can see the ending of this statement: "Pipe thread tape only."

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: MINI VENT

    Quote Originally Posted by Jerry Peck View Post
    It looks like that might make the minimum required height, it is also well within the 15 degrees of vertical it is required to be, has adequate space around it to allow for its removal and replacement, however, it is require to have pipe thread tape around its threads and that looks like pipe dope - which is not allowed.

    You can see the ending of this statement: "Pipe thread tape only."
    JP:

    Good call.

    Aaron


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: MINI VENT

    Aaron,

    I look at every one for pipe thread tape.

    For many years the plumber's used nothing, nada, and I wrote them up as not being sealed (all fittings and joints are to be "sealed", so they started gluing them in place (not only is that not 'pipe thread tape', but the Studor Vent is ABS and the piping was PVC, you should not use PVC cement on ABS ... so they started using pipe dope ... the dopes ).

    I had already been pointing out that they all state "Pipe Thread Tape Only", I had to teach the plumbers and municipal inspectors that "Pipe thread tape only" means, ... well ... "Pipe thread tape ONLY" ... NOT 'pipe dope' and not 'PVC cement'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •