Condensate from Condensing boiler
Condensate from high efficiency boilers is very acidic. Can it be plumbed directly into the home's sanitary drain or does it have to be treated first?
I was at a new home yesterday with 3 HTP high efficiency boilers being installed (500,000 btu each) and there is continuous condensate dumping from the units right into a sump well. Not sure if this won't affect the life of the sump pump.

Impressive installation....there are also a pair of 200 gallon indirect water heaters.

Similar Threads:
-
01-11-2009, 02:51 PM #2
Re: Condensate from Condensing boiler
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
01-11-2009, 04:32 PM #3
Re: Condensate from Condensing boiler
The condensate from 90% gas burning appliances is typically no stronger then urine and it is allowed to be discharged into the sanitary sewer system. The flue gases from the same appliances also has an acitic content, which is the resone for the PVC flue pipe.
-
01-11-2009, 04:40 PM #4
Re: Condensate from Condensing boiler
The "condensate" and the liquid produced from the "flue gases", as stated above, are one and the same thing, are they not?
As I said, it's my understanding that in Rhode Island and/or Massachusetts, at least, treating ("sweetening") the acidic condensate is required. I don't know about other states or regions.
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
01-11-2009, 05:28 PM #5
Re: Condensate from Condensing boiler
This question came up a while ago. I think most stated it was Ok for direct discharge in most areas. Some maybe not. Ok around here.
-
01-11-2009, 06:55 PM #6
Re: Condensate from Condensing boiler
It seems to be okay here, but then again so are a lot of things.
How big was that house? It must be gigantic. That much boiler capacity would heat most of my street.
Jim Robinson
New Mexico, USA
-
01-11-2009, 07:50 PM #7
Re: Condensate from Condensing boiler
Looks impressively nice ... until you start looking at the details ...
Is it just me, or do those sediment traps look like the caps on at the floor?
How on earth is one to unscrew them to empty the sediment trap?
-
01-11-2009, 07:53 PM #8
-
01-11-2009, 07:56 PM #9
-
01-11-2009, 09:11 PM #10
Re: Condensate from Condensing boiler
Ron,
Typically (i.e., "typically" means it is in the IRC commentary but spelled out in the IRC itself) the minimum drop is 3".
However, my point was that the shut off valve is installed upstream of the sediment trap to allow the gas to be shut off, the sediment trap unscrewed, emptied out, then re-installed ... and that there is - "looks like" - there is no room for that to be unscrewed and thus no way to realistically clean the sediment trap.
-
01-11-2009, 10:36 PM #11
Re: Condensate from Condensing boiler
Thanks Jerry. I ask that because i had a home the other day that had a drip leg but it was short like 1 inch.
Best
Ron
-
01-12-2009, 06:18 AM #12
-
01-12-2009, 06:23 AM #13
Re: Condensate from Condensing boiler
Here's another view of the boilers and a few other pics I took in the mechanical room....there is room to unscrew the caps. A friend of mine was over at the house on Sunday doing the control wiring. He did notice a problem with the mounting of one of the recirculation pumps as some of you will see below.
Also, the boiler installation is very tight. These units are meant to be stacked and doing so would have allowed a lot more room around the units. Originally, the job called for 2 boilers but it was increased to 3. This installation makes the job across the street from this home (see Munchkin and Chiller HVAC ) look tiny.





Last edited by Steve D'Gerolamo; 01-12-2009 at 06:32 AM.
-
01-12-2009, 06:33 AM #14
Re: Condensate from Condensing boiler
Last edited by Billy Stephens; 01-12-2009 at 07:28 AM. Reason: if to when
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
01-12-2009, 10:05 AM #15
Re: Condensate from Condensing boiler
The shaft on that lower pump is supposed to be horizontal, if I recall correctly.
I also believe that the PEX is supposed to come off the manifold straight, be strapped and supported, then bend.
I don't like that NM cable hanging and exposed like that to the pumps either, really should be in flexible conduit for protection (this is arguable position, so I am sure I will get arguments on it
).
-
01-12-2009, 10:18 AM #16
-
01-12-2009, 10:45 AM #17
Re: Condensate from Condensing boiler
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
08-22-2011, 10:07 AM #18
Re: Condensate from Condensing boiler
If all you can find is a short nipple on the drip leg, you are looking too hard. Technically, 3.5". These have room to screw off but I have rarely found a drip of anything on natural gas installations.
The circulator drive shaft should lay perpendicular to the pipe and horizontal in low pressure applications and MC is standard for wiring.
Condensate from condensing boilers has a pH between 4 & 5 (a lemon and an orange) and will not harm plastic waste pipe or septic system. If the condensate runs to an old cast iron drain where a softener or AC unit is not also drained erosion may be an issue...in a decade or two.
Electricians rarely do the near wiring.
-