Results 1 to 11 of 11
Thread: Notch in rafter
-
02-26-2009, 04:14 PM #1
Notch in rafter
This is borderline, would you call this out?
Thanks
Mat
Similar Threads:
-
02-26-2009, 06:01 PM #2
-
02-26-2009, 06:14 PM #3
Re: Notch in rafter
I would. if that ever splits it could come back on you... Is that pipe up on the rafter?
Best
Ron
-
02-26-2009, 08:41 PM #4
Re: Notch in rafter
I agree with Ron, I would call it out.
-
02-26-2009, 10:33 PM #5
Re: Notch in rafter
I don't believe I would call that out.
-
02-26-2009, 11:14 PM #6
-
02-27-2009, 09:56 AM #7
Re: Notch in rafter
Thansk guys. I found a section in the code which states it is acceptable.
-
02-28-2009, 07:20 PM #8
Re: Notch in rafter
Hi, Guys &
Definitely 'Butchered"...
I'd sure call it !
CHEERS
-Glenn Duxbury, CHI
-
03-01-2009, 10:55 AM #9
Re: Notch in rafter
Allot light around those pipes. Is the roof flashings in place.
If it was within guidlines it wouldn't go in my report.
-
03-02-2009, 02:20 PM #10
Re: Notch in rafter
There are other rafters that are close enough to it AND it is within the allowed notch (your statement) Then no reason to call it out.
-
03-09-2009, 08:03 PM #11
Re: Notch in rafter
IBC 2006- "2308.10.4.2 Notches and holes.Notching at the ends of
rafters or ceiling joists shall not exceed one-fourth the
depth. Notches in the top or bottom of the rafter or ceiling
joist shall not exceed one-sixth the depth and shall not be
located in the middle one-third of the span, except that a
notch not exceeding one-third of the depth is permitted in
the top of the rafter or ceiling joist not further from the
face of the support than the depth of the member."
Pretty much says it all.