Absence of Sub-Panel in Detached Shed
I called out the absence of a sub-panel in a detached shed today! I called it out because there is electrical in the shed, between 8-10 interior receptacles, with no panel in sight. I did this because I felt it would fall into the "in case of emergency" category. My question is, did I call it right? I appreciate your comments ahead of time.
Similar Threads:
-
05-12-2009, 11:54 AM #2
Re: Absence of Sub-Panel in Detached Shed
Unless there is a submarine in that other building it does not need a sub-panel.
However, it does require a disconnecting means in some enclosure, and that would be a panel, or even a "remote" "panel" to identify it as being "remote" from the main building's "panel".
You said there were 8-10 receptacles, but how many circuits?
From the 2008 NEC. (underlining is mine)
- 225.31 Disconnecting Means.
- - Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
- 225.32 Location.
- - The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section, the requirements in 230.6 shall be utilized.
- - - (there are 4 exceptions, now of which would apply to your installation)
-
05-12-2009, 12:29 PM #3
Re: Absence of Sub-Panel in Detached Shed
I would say as long as it is "BREAKERED" at the main panel, it would be ok. I see no reaxon for a sub panel, at the shed.
If that were a requirement, all detached garages would need a "sub panel".
Any electricans out there???
-
05-12-2009, 01:43 PM #4
Re: Absence of Sub-Panel in Detached Shed
codeman,
250.32(A) exception?
-
05-12-2009, 02:33 PM #5
Re: Absence of Sub-Panel in Detached Shed
Huh?
250.32(A) is about grounding electrodes and not about location of overcurrent protection.
The exception excepts out the grounding electrode under the conditions given.
The grounding electrode system is not even in the question.
Me thinks brian needs to read the code before responding as such.
-
05-12-2009, 02:36 PM #6
Re: Absence of Sub-Panel in Detached Shed
-
05-12-2009, 04:03 PM #7
Re: Absence of Sub-Panel in Detached Shed
codeman,
now read 225.36 exception! you just might learn something without me having to tutor you
-
05-12-2009, 04:21 PM #8
Re: Absence of Sub-Panel in Detached Shed
You really need to learn to read better, such as in my first post ...
... I covered that, yep.
No go back and read what I posted, heck, I'll quote it here again.
This is what YOU are referring to:
- 225.36 Suitable for Service Equipment.
- - The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
- - - Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.
brian, did you read that last sentence? Do you understand it yet?
Here is what Ed stated and what I am going on:
Don't get it yet?
Do you see where there would be a switch in there???
Maybe for a light, provided a light is installed (I would presume so, given that there is electrical in there) and I would presume there is a switch FOR THE LIGHT ... BUT NOT FOR "THE ELECTRICAL" to that shed, i.e., I doubt there is a switch which turns on and off all electrical to that shed.
That stated, or, in this case NOT STATED, then my original post stands.
You really need to wake up, read the post, read the response, read the code, then re-read the post and the response, ... maybe ... maybe ... you will begin to "get it" ... nah, too much to ask from someone like you.

-
05-12-2009, 04:53 PM #9
Re: Absence of Sub-Panel in Detached Shed
codeman,
i'll try to make it simple for the kid who went to school in the special little yellow bus! i am typing really slow for you!
a snap switch can control 8 to 10 receptacles. see also 225.38. we also allow the feed to begin at a gfi receptacle which serves as the disco and provides gfi protection to the rest of the outlets on the circuit. no grounding electrode system,no sub-panels,service or non -service panels required. this is quite common in anywhere other than jerry's world!
-
05-12-2009, 05:19 PM #10
Re: Absence of Sub-Panel in Detached Shed
b-r-i-a-n,
I w-i-l-l m-a-k-e i-t r-e-a-l s-i-m-p-l-e f-o-r y-o-u ...
"can" does not mean "it is".
Get a grip man and start learning, that includes reading, and understanding what you read, and then understanding that you do not know it all, and that just because something "can" be done does not mean "it is" done.
Let Ed solve your puzzle for you which you cannot figure out ...
Ed, was there a switch which shut the power all to all the receptacles?
Yes and I will have to learn to read between the lines.
No and brian will n-e-e-d t-o l-e-a-r-n t-o r-e-a-d and comprehend what he is reading.
-
05-12-2009, 06:35 PM #11
-
05-12-2009, 06:45 PM #12
-
05-12-2009, 09:13 PM #13
-
05-13-2009, 08:12 AM #14
-
05-13-2009, 08:18 AM #15
Re: Absence of Sub-Panel in Detached Shed
-
05-13-2009, 11:05 AM #16
Re: Absence of Sub-Panel in Detached Shed
-
05-13-2009, 12:00 PM #17
Re: Absence of Sub-Panel in Detached Shed
ed,
your welcome! thanks for providing a question for entertainment and education. i think it meets code but i,m just a schmitt so what do i know?
-
05-13-2009, 12:24 PM #18
Re: Absence of Sub-Panel in Detached Shed
Probably a whole lot, Brian! Thanks again!
-
05-13-2009, 01:13 PM #19
Re: Absence of Sub-Panel in Detached Shed
[quote=Jerry Peck;84319]b-r-i-a-n,
Get a grip man and start learning, that includes reading, and understanding what you read, and then understanding that you do not know it all, and that just because something "can" be done does not mean "it is" done.
codeman,
i am happy that you have admitted to yourself and everyone else that you are dealing with your "issues"
-
05-13-2009, 03:01 PM #20
Re: Absence of Sub-Panel in Detached Shed
Ed,
You are welcome.
brian,
I don't read into what is written, and when I do I state so, such as "I presume ... " and state what I am reading into it and presuming.
Unlike you who always reads things into what it posted and not there, and, this one time, YOU GOT IT RIGHT!
Way to go brian, you finally got one right!
-
05-13-2009, 04:47 PM #21
Re: Absence of Sub-Panel in Detached Shed
thanks jerry.i think