Results 1 to 5 of 5
Thread: Conflicting Suretest results
-
09-24-2009, 06:50 AM #1
Conflicting Suretest results
120V circuit to detached garage in conduit from load side panel in house.
My 61-165 indicated an open ground (and a correct ground everywhere else I tested inside the house), when further investigation by others indicated a correct ground I went back and retested with my 61-058, which indicated a correct ground.
Defective 165, or ????
Similar Threads:Last edited by Michael Thomas; 09-24-2009 at 06:59 AM.
-
09-24-2009, 07:55 AM #2
Re: Conflicting Suretest results
Flakey ground wire connection somewhere in supply. Tool problem. Bad receptacle ground contact.
I've seen many (mainly older) receptacles that have a bad ground contact on the front side. The top or bottom may be bad and the other works just fine.
-
09-24-2009, 08:11 AM #3
Re: Conflicting Suretest results
-
09-24-2009, 08:19 AM #4
Re: Conflicting Suretest results
You can pull an outlet at your home and play with the wires to see if unit
showing what you have set up...
Best
Ron
-
09-24-2009, 05:35 PM #5
Re: Conflicting SureTest results
Also, the 3-light SureTest tester, while being a better grade of 3-light tester, is not the same as the circuit analyzer capacity built into the SureTest 61-165, which is likely picking up on abnormally high resistance in the ground circuit, showing that as a "open ground", whereas the 3-light SureTest is not testing the resistance of the ground, but probably just voltages between the prongs on its plug, and if there is voltage hot-to-ground the 3-light tester is saying "looks okie dokie to me".
The SureTest 61-165 is saying, 'Sure there is voltage hot-to-ground, but the resistance of the ground is way too high for what it should be, so it is "no tickee no laundree". '
At least that is my GUESS. I think Bill is right, there is a problem in the ground/receptacle ground.



Reply With Quote

Bookmarks