2 Flues
I'm combing through IRC 2427 and do not see anything that would cover this.
These are the flue terminations for the water heater and an old Sears wall heater. I personally don't like them being so close, but cannot "prove" it.
I included the other photo as a bonus for the inspectors out there.
Bruce
Similar Threads:Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
Home Inspections in the Tyler and East Texas area
-
08-07-2009, 01:52 PM #2
Re: 2 Flues
Can't help on the Code issue for that. Don't like it either though. I would look more for writing height above roof on the shorter one, lack of critter guard and overall flashing detail.
-
08-07-2009, 01:54 PM #3
Re: 2 Flues
J.B.,
Unapproved Vent Cap
That Wagon Train ( half round & affixed piece of sheet metal.)
.
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
08-07-2009, 02:14 PM #4
Re: 2 Flues
Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
Home Inspections in the Tyler and East Texas area
-
08-07-2009, 02:22 PM #5
-
08-07-2009, 06:06 PM #6
Re: 2 Flues
-
10-15-2009, 08:45 AM #7
Re: 2 Flues
Jerry, Had another of the covered wagon vent caps on a 2006 water heater, so I made note of it. I am looking for the Type B gas vent cap requirement in the IRC. Could you point me in the way?
Also, I pulled up the installation instructions for a particular water heater and it says refer to the gas supplier or National Fuel Gas Code ANSI Z223.1/NFPA 54 for venting requirements.
The seller is stating that his plumber knows more about the code than I do (maybe or maybe not) So I am looking for specific knowledge.
Bruce
Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
Home Inspections in the Tyler and East Texas area
-
10-15-2009, 10:30 AM #8
Re: 2 Flues
Bruce,
- M1804.2 Termination. Vent termination shall comply with Sections M1804.2.1 through M1804.2.6.
- M1804.2.1 Through the roof. Vents passing through a roof shall extend through flashing and terminate in accordance with the manufacturer’s installation requirements.
Here is one example: http://www.duravent.com/docs/instruct/L204A_apr00.pdf
Go to Fig 12 on page 8 of 20 ... on the left you will see the installation sequence description, right after "Add sufficient Pipe Sections to attain the height specified in Table 2." you will find ""To connect the Top to the pipe, hold Top by its collar, slide collar over locking lugs of pipe, and twist-lock clockwise. Tops of ... " (bold is theirs) - on the right see the two listed TOPS which are interchangeable: the High Wind Top and the DuraCap Top.
-
10-16-2009, 09:26 AM #9
Re: 2 Flues
Bruce,
I forgot these the other day:
- G2427.6 (503.6) Gas vents. Gas vents shall comply with Sections G2427.6.1 through G2427.6.11. (See Section G2403, Definitions.)
- - G2427.6.3 (503.6.3) Roof penetration. A gas vent passing through a roof shall extend through the roof flashing, roof jack or roof thimble and shall be terminated by a listed termination cap.
And:
- G2427.6.6 (503.6.6) Roof terminations. Gas vents shall extend through the roof flashing, roof jack or roof thimble and terminate with a listed cap or listed roof assembly.
-