Results 1 to 20 of 20
Thread: Neutrals and grounds
-
10-01-2009, 11:27 AM #1
Neutrals and grounds
Last edited by Ryan Stouffer; 10-01-2009 at 03:23 PM.
-
10-01-2009, 12:56 PM #2
Re: Neutrals and grounds
New post
-
10-01-2009, 12:58 PM #3
Re: Neutrals and grounds
They occupy the same bar in the service equipment or main panel.
-
10-01-2009, 02:34 PM #4
Re: Neutrals and grounds
No offense meant, but shouldn't common topics like this be covered in the training courses? Isn't there any requirement to shadow an experienced inspector before doing this on your own?
I commend you for asking questions as that is how we all learn. But how good can the inspection be when the common topics still need to be covered?
-
10-01-2009, 02:51 PM #5
Re: Neutrals and grounds
Couple of black conductors there need to be properly marked as grounded/neutral conductors.
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
10-01-2009, 03:28 PM #6
-
10-01-2009, 03:40 PM #7
Re: Neutrals and grounds
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
10-01-2009, 04:13 PM #8
Re: Neutrals and grounds
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
10-01-2009, 04:27 PM #9
-
10-01-2009, 04:59 PM #10
Re: Neutrals and grounds
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
10-02-2009, 04:20 PM #11
Re: Neutrals and grounds
If the wires are feed in thru conduit, I believe you would have to duct seal
around all the wires to seal the conduit openning.
Last edited by Robert Mattison; 10-03-2009 at 04:50 PM.
-
10-02-2009, 04:43 PM #12
-
10-02-2009, 05:04 PM #13
Re: Neutrals and grounds
-
10-03-2009, 02:50 AM #14
Re: Neutrals and grounds
My reply in my last post comes from, the NEC 2008 edition:
300.5(G) Raceway Seals
300.7 Raceway Exposed to Different Temperatures
-
10-06-2009, 06:45 PM #15
Re: Neutrals and grounds
Borrowing the thread for a moment, for today's jewel of a neutral.... I now return you to your regularly scheduled programming....
-
10-07-2009, 03:37 AM #16
Re: Neutrals and grounds
BTW, what section of the NEC governs the splicing of SECs?
-
10-08-2009, 05:09 PM #17
Re: Neutrals and grounds
-
10-28-2009, 07:32 AM #18
Re: Neutrals and grounds
Jerry, Since I'm a little north of you, I'm not familiar with the NEC but doesn't that sentance refer to splicing of the actual feeder cable (ie: extending it) and not splicing the branch circuit wires to the feeder (as in lack of neutral bar) ?
Also, does the NEC allow all the branch circuit wiring to enter and pass through the main-switch compartment ?
Just curious.
-
10-28-2009, 04:13 PM #19
Re: Neutrals and grounds
Joe,
The question was about "service entrance conductors", thus the reference to splices for service entrance conductors, not feeders or branch circuits.
No. I believe you are referring to using the panel as a "raceway", i.e., "does the NEC allow all the branch circuit wiring to enter and pass through", and all the conductors in the panel are to be terminated in that panel, either at the grounding terminals, neutral terminals, or at an overcurrent device. This means that "passing through" is not allowed.Also, does the NEC allow all the branch circuit wiring to enter and pass through the main-switch compartment ?
-
10-28-2009, 05:34 PM #20
Re: Neutrals and grounds
Sorry Jerry, I thought we were both talking about the photos in post # 15 above.



Reply With Quote