Results 1 to 7 of 7
  1. #1
    Jon mackay's Avatar
    Jon mackay Guest

    Default Copper pipe hangers

    I'm second guessing myself yet again.
    You can't use these hangers on copper right? This is a new installation.
    They should be those wire type with the vinyl or rubber sleeve for protection correct?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    A.D. Miller's Avatar
    A.D. Miller Guest

    Default Re: Copper pipe hangers

    SECTION P2605
    SUPPORT
    P2605.1 General. Piping shall be supported in accordance
    with the following:
    1. Piping shall be supported to ensure alignment and prevent
    sagging, and allow movement associated with the
    expansion and contraction of the piping system.
    2. Piping in the ground shall be laid on a firm bed for its
    entire length, exceptwhere support is otherwise provided.
    3. Hangers and anchors shall be of sufficient strength to
    maintain their proportional share of the weight of pipe
    and contents and of sufficient width to prevent distortion
    to the pipe. Hangers and strapping shall be of approved
    material that will not promote galvanic action. Rigid support
    sway bracing shall be provided at changes in direction
    greater than 45 degrees (0.79 rad) for pipe sizes 4
    inches (102 mm) and larger.
    4. Piping shall be supported at distances not to exceed those
    indicated in Table P2605.1.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Copper pipe hangers

    Quote Originally Posted by Jon mackay View Post
    You can't use these hangers on copper right?
    The don't need rubber sleeves or anything like that, but that is not allowed for several reasons, first, those are not copper (at least those straps do not look like they are copper) and will create corrosion from dissimilar metal contact, and, secondly even if they were copper they would not be allowed to be installed and used as shown.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Dec 2008
    Location
    Montreal, QC, Canada
    Posts
    63

    Default Re: Copper pipe hangers

    I have seen this done before ... however never so sloppy and at the risk of sounding stupid here goes................

    3. Hangers and anchors shall be of sufficient strength to
    maintain their proportional share of the weight of pipe
    and contents and of sufficient width to prevent distortion
    to the pipe. Hangers and strapping shall be of approved
    material that will not promote galvanic action.
    Rigid support
    sway bracing shall be provided at changes in direction
    greater than 45 degrees (0.79 rad) for pipe sizes 4
    inches (102 mm) and larger.

    The strapping material in question is of such a type that it will promote galvanic corrosion.

    As such it somehow need to be insulated as such to meet the code requirement. I have seen this done by wrapping vinyl or electrical tape around the pipe or strapping to isolate the two materials.

    In my opinion... too much work for nothing... proper clamps are probably, faster, cheaper and easier at the end of the job.

    Adas long as the two materials are properly insolated and that the support is adequate I would not find fault with it.


  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Exclamation Re: Copper pipe hangers

    They do make copper plated pipe strapping. I keep a roll on my truck. Still, proper rigid split ring clamps or brackets preferred.
    Bob

    Keep the fire in the fireplace.

  6. #6
    David Bell's Avatar
    David Bell Guest

    Default Re: Copper pipe hangers

    Looks like another quality plumbing job by a tinknocker,,notice the black iron reducing coupling on the high vent?


  7. #7
    Jon mackay's Avatar
    Jon mackay Guest

    Default Re: Copper pipe hangers

    Thank you David..
    Too funny, yeah this system was installed about 4 days before the inspection and it had 2 large leaks and 1 minor leak.. Nice work!!


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •