Results 1 to 29 of 29
Thread: Garage service door width
-
03-13-2010, 06:30 AM #1
Garage service door width
Hello all...I am wondering if there is a minimum width requirement for a garage service door to the interior? Any help?
Similar Threads:
-
03-13-2010, 08:45 AM #2
Re: Garage service door width
-
03-13-2010, 09:42 AM #3
Re: Garage service door width
While SP may be correct about the width, some local regulations do set minimum heights on all doors. One example is from the State of Connecticut:
The required exit door shall be a side-hinged door not less than 3 feet in width and 6 feet, 8 inches in height. Other doors shall be permitted to be side-hinged, swinging, sliding, bi-fold or revolving doors, shall not be required to comply with the minimum door width and shall be permitted to be not less than 6 feet, 6 inches in height (IRC R 311. 4. 2, 2003 IRC Portion of the 2005 State Building Code)
So then, be certain to check with the local codes and amendments in order to be safe.
-
03-13-2010, 10:27 AM #4
Re: Garage service door width
"There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
www.ArnoldHomeInspections.com
-
03-13-2010, 02:00 PM #5
Re: Garage service door width
Presuming you are referring to an attached garage (service door to the interior).
Is there a "man door" from the garage to the exterior? Is there service equipment for the attached structure in the garage? If present is this equipment separated from the general garage space by walls and/or doors?
For example electrical panel, HVAC equipment, DWH, etc. Accessibility and egress requirements may be found in other areas of the codes.
If the "service door to the interior" refers to the "man door" for a free-standing garage, and the door is for access from the outside to the interior of the garage, please clarify - that's a "horse of a different color".
Also please indicate presence or lack of window in garage and window size.
Occupied space.
Also please clarify if you are referring to a single family residence/garage, duplex, multi-family, condo, etc. commercial garage, or if the "garage" is an auxilliary structure to a manufactured home lot, etc.
I'm assuming from your "garage" description it is safe to assume we are not discussing a smaller auxilliary structure that could be considered a "shed" and due to its smaller size and height would meet certain exceptions to requiring a separate service door ("man door").
Note your location California. Also presuming not a HUD assisted property.
Last edited by H.G. Watson, Sr.; 03-13-2010 at 02:12 PM.
-
03-13-2010, 03:02 PM #6
Re: Garage service door width
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
03-13-2010, 04:31 PM #7
Re: Garage service door width
Gunnar,
Notice I asked a series of questions, and explained there were a number of areas of the California Codes which might address this.
Depends upon the series of answers.
Recall I inquired if the garage was attached or detached auxiliary structure, and if he was referring to a door between garage & interior of the home/common hall of condo, etc. or referring to service door ("man door")from the outdoors to the interior of the garage?
Note I mentioned Occupiable space. I also inquired as to what type of property the inquiry was about (not assuming single family residential single lot with attached garage - he hasn't said that ... yet
).
Further note I inquired if other equipment in garage. Lets say for example laundry facilities (although I inquired about DWH, HVAC, electrical panel, etc.).
Do you see some of the directions I was heading? Many different areas.
I'm waiting for the answers.
-
03-13-2010, 06:04 PM #8
-
03-13-2010, 07:01 PM #9
Re: Garage service door width
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
03-13-2010, 09:20 PM #10
Re: Garage service door width
thank you
-
03-13-2010, 11:39 PM #11
Re: Garage service door width
LOL.
Ron Bishop,
If S.F. Res, detached or attached garage and you're asking about the doors for a person to exit the garage area (occupied not habital space): An "exit door" shall be capable of opening so that the clear width is not less than thirty-two (32) inches and not less than six feet, eight inches (6'8") in height.
Horizontal Sliding Doors are okay.
Overhead doors do not count. Operating mechanisms must be 34-48" above the finished floor. Exit doors from garage must be operable without a key - this excludes deadbolts locks if the key side is towards the inside of the garage.
You'll find it in Chapter 10 of Title 24 California Building Code 2007.
1001.1, 1002.1, 1008.1.1, 1008.1.3.3, 1008.1.8, 1008.1.8.2
and if attached garage see also: 1014.2.
If you have equipment in garage, laundry, furnace closet, electrical panel, etc. there are more provisions to consider on doors, also if other than R1.
Last edited by H.G. Watson, Sr.; 03-13-2010 at 11:49 PM.
-
03-14-2010, 09:28 AM #12
Re: Garage service door width
JR:
Most pre-hung swing doors allow for a greater than 90 degree swing (105 at least usually). Not really following your question or logic on the "stop" issue. Also don't know why you're asking without having first actually read Chapter 10 of the California Code, which was specific to the location of the original poster of the topic; or why you'd care since you're in TX and the response was specific to the California Code. There are a number of other factors not addressed by the OP which may influence the requirements for the minimum clear openings for exit door(s) from garage.
Clear Width means that even the door hardware may not incroach the path. There are a few exceptions and some factors which may increase the minimum clear width and height - they were not addressed.
Clear Width refers to the opening/path and in no way refers to the actual dimensions of the door blank itself?!?!??
To provide the clear width a minimum sized exit door in question and therefore the hinge would necessarily have to open beyond 90 degrees.
Therefore you would not be permitted to install or adjust a door or hinge stop in such a manner which restricted or encroached upon the minimum Clear Width, and may not allow door hardware, adornments upon the door, doorway, area storage, furniture, fixtures, wall decor, plantings, or any other obstruction/encroachment which would hinder that minimum clear width at any time, damaged hinges or pins, misalignments, etc. which restricted or present stress which required more than the maximum force pressures required to operate the door and acquire the minimum clear width would also have to be addressed/corrected. There is more to a "means of egress system" than just the exit door itself.
Originally Posted by 2007 CBC 1001.1
If you are interested, the "definitions" section was also cited in the prior post, have a read.
Finally, are you not familiar with "full extension hinges"?
Last edited by H.G. Watson, Sr.; 03-14-2010 at 09:46 AM.
-
03-15-2010, 08:55 AM #13
Re: Garage service door width
JR,
Confusion/failure to communicate arising between "the stop" and "a door stop". You're asking about "the stop" rest which stops the face of the door when closed, not "a door stop" which limits the maximum open swing radius of a door. Okay, lets address your question. (Keeping in mind we're presuming single family residence occupancy load 10 or less, but we still don't know if attached or detached garage, or if there are other systems within, closets, walls, doors or other factors within, or in the path of egress to consider):
You'll find more details and exceptions throughout Chapter 10.
Originally Posted by 2007 Calfornia Building Code
Although the door blank may be smaller You'll find the clear openings for prime (exterior) and rated doors are generally a bit larger and the stop to door face is sufficient with 2-8 (32") doors. The measurements you're providing are generally what is found for the door blank itself, not the clear opening, unless the hinge plate has been shimmed or isn't sufficiently tightened (post install) to the hingle gasket (if applicable).
Last edited by H.G. Watson, Sr.; 03-15-2010 at 09:10 AM.
-
03-15-2010, 09:35 AM #14
-
03-15-2010, 10:10 AM #15
Re: Garage service door width
Nope. Not only must the hardware be within floor measurement limitations, the means to operate the door (unlatch, provide for opening) and the weight/force required still has to meet the requirements (30 lbs/15 lbs force). The section & its exceptions you refer to are regarding the otherwise required side-hinge SWING to the door, that exception allows for a SLIDING door to be used or a folding door, it does not provide for an OH door for the required exit door.
If you finished reading the section following the exceptions it says:
"The opening force for interior side-swinging doors without closers shall not exceed a 5-pound (22 N) force. For other side-swinging, sliding and folding doors, the door latch shall release when subjected to a 15-pound (67 N) force. The door shall be set in motion when subjected to a 30-pound (133 N) force. The door shall swing to a full-open position when subjected to a 15-pound (67 N) force. Forces shall be applied to the latch side."
The entirety of Ch. 10 & if applicable Ch. 11A or 11B.
Here's a quote from a ruling:
Required Exit Doors in Garages.
The California Building Code requires that every portion of the building have a code complying means of egress.
Requirements for minimum exiting from a residential garage.
The CBC (2007) requires that exit doors be openable from the inside without the use of a key, or any special knowledge or effort. Operating mechanisms must be installed 24" to 48" above the finished floor.
Therefore an overhead garage door does not meet the requirements for an exit door.
An exterior key-operated deadbolt is often installed at the door between the garage and the residential portion of the building for security purposes. In this case, the door between the house and the garage cannot serve as a complying exit FROM the garage because the deadbolt lock requires a key from the garage side to open.
An "exit door" shall be capable of opening so that the clear width is not less than thirty-two (32) inches and not less than six feet, eight inches (6'8") in height.
For the above reasons, it is often necessary to provide an additional door that opens directly to the exterior, which is openable from the garage side without the use of a key, or any special knowledge or effort.
Last edited by H.G. Watson, Sr.; 03-15-2010 at 10:21 AM.
-
03-15-2010, 10:20 AM #16
Re: Garage service door width
-
03-15-2010, 10:24 AM #17
-
03-15-2010, 11:03 AM #18
-
03-15-2010, 11:39 AM #19
Re: Garage service door width
Argue with the commission. The entirety of Ch. 10 & if applicable "R" occupancy group, potentially Ch. 11A or 11B.
Get your headroom rules/ceiling and horizontal projections regarding the opening and path as well.
Then get real and get your head out of the hole its in. Try clarifying attached or detached. Then try to understand the original post hasn't even clarified an occupancy type for the question. "U" group, "S" group or "R" group if attached. If you cannot read a short chapter in its entirety and retain the information long enough to realize what the Code says, I posted the ruling from a Bulletin.
You're wrong on representation as to what the section you cited actually says, and it does not stand alone.
-
03-15-2010, 12:59 PM #20
Re: Garage service door width
h.g. aka jerk azz,
the original poster is a hi and would not normally be inspecting chapter 11a or 11b structures,which don't include s.f.d.'s. i could care less about quotes from some comission. jurisdictions i have worked for and all local jurisdictions in the norcal area allow the overhead door to serve as an exit door for an attached or detached garage for an sfd,period. go scream or rant to a chicken
-
03-15-2010, 01:44 PM #21
Re: Garage service door width
Condos, other multi-family dwellings are inspected by HIs every day. (11A). SFDs with a person confined to bed, etc. - exit door requirements also change. HUD financed, guaranteed, or otherwise "assisted" properties are common.
7'6" clear ceiling area, headroom min 80" due to horizontal encroachment in path not to be encroached more than 50 percent.
Name a jurisdiction under 2007 CBC that approves special knowledge and greater forces than the unammended California code permits, control out of permitted floor height for same, or that applies and ignores different sections for attached and detached garages on lots with residential occupancy groups regarding the strength and forces required to open.
Don't forget to provide us with the individual NAMES at those offices too.
During the interim, as a Seinfield character said: "NO SOUP FOR YOU!"
Last edited by H.G. Watson, Sr.; 03-15-2010 at 02:04 PM.
-
03-15-2010, 02:17 PM #22
-
03-16-2010, 04:21 AM #23
-
03-16-2010, 06:56 AM #24
Re: Garage service door width
Talk about stretching one simple question into a thread about nothing that the original poster asked just so one can show how smart they are in areas that don't even matter.........WOW!
Now that I think about it......did the window that has nothing to do with anything, that's not there, meet the energy code?
This site is entertainment at the least!
-
03-16-2010, 11:30 AM #25
Re: Garage service door width
And the sad thing is HG is wrong on most of his interpretations of the CBC.

Jerry McCarthy
Building Code/ Construction Consultant
-
03-16-2010, 07:39 PM #26
Re: Garage service door width
Really WC Jerry!
Why don't you stick your neck out and explain EXACTLY where and WHAT is wrong?
I'm waiting. Since you failed to grasp the particulars of another brian's garage conversion post...I'm really interested to know just WHERE.
YOU POINT IT OUT, EXACTLY. The Code language is NOT ambiguous, only the poster's DETAILS were ambiguous.
Fact set and citations - Lets have it - RIGHT HERE.
-
03-16-2010, 07:51 PM #27
Re: Garage service door width
It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
Billy J. Stephens HI Service Memphis TN.
-
03-17-2010, 01:30 PM #28
Re: Garage service door width
Sorry to disappoint Billy, but Scott is right in that this thread has gotten out of hand, too long, argumentative, and worse….. boring..
We need to move on.
Jerry McCarthy
Building Code/ Construction Consultant
-
03-17-2010, 03:02 PM #29
Re: Garage service door width
Because it was NOT wrong.



Reply With Quote