Thread: exposed cable run
-
03-31-2010, 07:53 AM #1
exposed cable run
Is extra protection required here?
Similar Threads:
-
03-31-2010, 07:55 AM #2
Re: exposed cable run
Nice hand rail...
They should have ran it with the stairs
Best
Ron
-
03-31-2010, 09:09 AM #3
-
04-12-2010, 07:44 PM #4
Re: exposed cable run
Well, I don't think that's Mike Holmes approved....
-
04-12-2010, 08:47 PM #5
Re: exposed cable run
The cable should be repalced with conduit or re-routed through wall cavity.
-
04-13-2010, 05:57 AM #6
Re: exposed cable run
334.15 Exposed Work.In exposed work, except as provided
in 300.11(A), the cable shall be installed as specified
in 334.15(A) through (C).
(A) To Follow Surface.The cable shall closely follow the
surface of the building finish or of running boards.
(B) Protection from Physical Damage.The cable shall be
protected from physical damage where necessary by rigid
metal conduit, intermediate metal conduit, electrical metallic
tubing, Schedule 80 PVC rigid nonmetallic conduit, or
other approved means. Where passing through afloor, the
cable shall be enclosed in rigid metal conduit, intermediate
metal conduit, electrical metallic tubing, Schedule 80 PVC
rigid nonmetallic conduit, or other approved means extending
at least 150 mm (6 in.) above the floor.
Looks like (A) has been followed. Physical protection is a judgement call, but, IMO the cable could be possibly damaged by a vacuum.
-
04-13-2010, 07:53 AM #7
Re: exposed cable run
Anywhere a dog can chew on it should have protection.
But like Jim says, it's a judgement call and the code leaves it up to "where necessary".
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
04-13-2010, 08:50 AM #8
Re: exposed cable run
it there to hang socks for drying