Thread: Can AFCI breaker have two wires?
10-19-2010, 04:03 PM #1
Can the AFCI breaker have two hot wires installed into one lug? Thanks
10-19-2010, 04:47 PM #2
Re: Can AFCI breaker have two wires?
The lug on the breaker is listed for a single conductor. The correct way to wire this would be to install a pigtail on the breaker and wire nut the 2 conductors to it.
This "fix" appears to have been made to Get AFCI protection on a multiwire branch circuit. GE makes a new style AFCI that can be used on this type circuit - two are used and only one requires the neutral connection, but a handle tie is required between the two.
10-19-2010, 06:37 PM #3
You should also note whether that Siemens AFCI breaker is allowed to be used in that enclosure.
10-20-2010, 06:42 AM #4
10-20-2010, 07:33 AM #5
10-20-2010, 07:46 PM #6
Good point, I "forgot" about the circuit breaker that would trip in an overload situation.
I guess if you consider what an AFCI breaker is supposed to do, there wouldn't be a problem connecting 2 wires as the issue with 2 wires is arcing. If you are going to double tap a breaker, the AFCI would be the one to double tap.
10-20-2010, 08:25 PM #7
The default rule is ONE per terminal, connector, lug, etc. when it comes to conductors; UNLESS INDICATED for more than one. INDICATED means marked or labeled.