Thread: Boiler vent size increase
11-30-2010, 11:10 AM #1
Is it always the case that the boiler vent size must increase when you add a water heater vent or are there exceptions?
In this case, a 150,000 BTU Boiler with 40,000 BTU Water heater.
I was thinking it needs to increase but wanted to double check.
Thanks..
11-30-2010, 08:03 PM #2
Re: Boiler vent size increase
Jon,
NFPA 54 is pretty clear on venting 2 natural draft appliances but first,
is it a masonry chimney and if so inside or outside?
chimney size and height?
any other appliances?
what is the connector sizes?
it looks like 3" into 6"?
what part of USA are you in?
Jack
MGF 3828
JGF 3910
12-01-2010, 06:15 AM #3
It is a masonry chimney that is an exterior mount.
The height is approximately 28' - 30'
3" into 6"
No other appliances
Binghamton, NY
Thank you Jack
12-01-2010, 09:21 AM #4
jon,
what size is the chimney? 12 x 12? 24 x 24?
thanks
jack
12-01-2010, 10:19 AM #5
12 x 12 is the chimney flue size.
12-03-2010, 06:21 AM #6
Jack,
were you able to determine the requirements with the information?
Thank you,
JOn