Results 1 to 17 of 17
Thread: Electrical Panel
-
02-01-2011, 07:04 PM #1
Electrical Panel
Couple questions ?? I made an inspection and noticed double tapping on the electrical panels. Somewhere I thought I heard that you could double up with neutrals to neutrals or ground to ground. But NOT a neutral with a ground.
Not sure True or False ??
See photos
Similar Threads:
-
02-01-2011, 07:12 PM #2
Re: Electrical Panel
Grounds are ok to double (or triple in some cases), if allowed by the panel's manufacturer. Current carrying conductors (hot & neutral) are not.
The problem was with the wording in the past NEC. The wording essentially stated that terminals for more than one conductor should be labeled by the panel's manufacturer. If you look at the label, you will find that they allow multiple grounding conductors under a single terminal screw, but not multiple grounded. As a result, many electricians and building inspectors believed that multiple neutrals were ok when they were not.
I believe that in the 2002 NEC, the wording was changed so that it was clear that multiple neutrals could not be secured under a single terminal screw. I do not have the specific code sections in front of me.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
02-01-2011, 08:49 PM #3
Re: Electrical Panel
I don't have my 2011 code book in front of me but I believe the section you are looking for is 408.41. If you have the handbook it explains why only one neutral per lug is used. When troubleshooting a circuit with two neutrals under the same lug the circuit you are not working on could still be energized. Keith
-
02-02-2011, 06:40 AM #4
Re: Electrical Panel
-
02-02-2011, 07:34 AM #5
Re: Electrical Panel
Even more of an issue with doubled neutrals is the problems that arise if a multi wire circuit is involved.
Another common misconception seems to be that if the hot wires are landed on a breaker that allows 2 wires to be terminated on it that the neutrals can be under the same screw. The NEC says otherwise.
-
02-02-2011, 07:38 AM #6
Re: Electrical Panel
-
02-02-2011, 08:06 AM #7
-
02-02-2011, 08:31 AM #8
Re: Electrical Panel
-
02-02-2011, 10:00 AM #9
Re: Electrical Panel
I mis-understood the intent of your question Scott.
-
02-02-2011, 05:42 PM #10
Re: Electrical Panel
Scott;
These were (2) 200 amp panels, 240 volts side by side in the garage utility room. They were practically the same. I'm assuming they were service panels. All the entrance lines were underground.
-
02-02-2011, 05:49 PM #11
Re: Electrical Panel
My guess would be that those are both downstream / branch / sub panels and the neutrals and grounds shouldn't be bonded but the picture is pretty blurry.
-
02-03-2011, 05:03 AM #12
-
02-03-2011, 06:44 AM #13
-
02-03-2011, 10:17 AM #14
Re: Electrical Panel
WRT multiple neutrals under a single terminal, see: http://paragoninspects.com/articles/...e_neutrals.pdf
-
02-03-2011, 10:59 AM #15
Re: Electrical Panel
Good link Michael !!!
Thanks
-
02-03-2011, 02:41 PM #16
-
02-03-2011, 03:50 PM #17



Reply With Quote


Bookmarks