    Default Re: Bonding to panel

    I'm going out on a limb here saying that I don't believe the manufacturer intended their equipment to be used in that manner.


  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Bonding to panel

    If that is the CATV, I think that it needs to be grounded and not bonded. Just like the telephone line. The need to have a grounding rod and then that rod is bonded to the main electrical ground. You will also see it attached to the main grounding conductor in some areas.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Bonding to panel


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Bonding to panel

    "in this fashion"

    Absolutely not!

    It needs to be bonded or grounded directly to the grounding electrode system.

    Can it be bonded to a component which is grounded to the grounding electrode system? Yes, such as the rigid metal riser.

    Do not, however, drive a separate ground rod (and those little metal stakes they drive in are not ground rods, ground rods are in the ground a minimum of 8 feet and at least 1/2" diameter) ... unless that ground rod is bonded back to the grounding electrode system with a grounding electrode conductor of the same size as the main grounding electrode conductor (i.e, not bonded with a small #12 wire).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Bonding to panel

    The diagram at Mike Holt site's lists "service equipment enclosure" as a allowed grounding point, is there a correct (approved) way to perform the attachment to the exterior of the enclosure?