Results 1 to 11 of 11
Thread: Outlet spacing along glass wall?
06-06-2013, 10:01 AM #1
What are the requirements for outlets along a wall that is floor to ceiling glass(residential). I know the 6'/12' rule for wall but am not sure how this applies to glass walls.
Thanks Joe
06-06-2013, 01:54 PM #2
Re: Outlet spacing along glass wall?
06-06-2013, 02:07 PM #3
Thanks will do.
06-06-2013, 05:11 PM #4
What Scott said, but a wall is a wall same rules apply. You may need a floor receptacle outlet if putting it in the wall will not work.
06-06-2013, 06:02 PM #5
My experience is that I see floor outlets. To build a wall that is glass I would put in floor outlets. Just makes it nicer if you need an outlet, if nothing else.
06-07-2013, 05:06 PM #6
Just going from memory from my electrical course, the rule does not apply where there are windows... at least here in Ontario. A receptacle is required every 12 feet of wall, excluding under windows.
Like I said, going from memory only... I might be wrong.
06-07-2013, 07:18 PM #7
Well ... he does have "ca" as his location ... but is that for Canada or for California?
The NEC requires that spacing at walls, if the glass is fixed in place then receptacles would be required, but could be floor receptacles. If the glass is operable, like a sliding glass door, then no receptacle would be required.
06-07-2013, 07:47 PM #8
06-07-2013, 11:22 PM #9
06-08-2013, 07:46 AM #10
Floor outlets to be counted in the calcs for wall spacing must be within 18 inches of the wall
06-11-2013, 01:59 PM #11
Just an additional note: The fixed portion (non-sliding pane) of a sliding door or door wall is also 'wall space' to be included in the 6' - 12' & 2' rule.