Results 1 to 4 of 4
  1. #1
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default radon fan wiring

    I'm digging for my radon mitigation manual but can't find it right now. I don't install the equipment but occasionally inspect it.

    Is it acceptable to have the fan wired via an appliance cord/plug that runs from the exterior through the wall to the interior where it's plugged into a receptacle?

    All of the other systems I've seen are hardwired. I'm wondering if there is a violation of sorts with running appliance cord to an exterior location.

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: radon fan wiring

    Wait...I did just find the following. (pic from manual)

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  3. #3
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: radon fan wiring

    Flexible cords are not allowed to pass through walls, doorways & such, here is a copy & paste from the 2008 NEC:

    400.8 Uses Not Permitted. Unless specifically permitted
    in 400.7, flexible cords and cables shall not be used for the
    following:
    (1) As a substitute for the fixed wiring of a structure
    (2) Where run through holes in walls, structural ceilings,
    suspended ceilings, dropped ceilings, or floors
    (3) Where run through doorways, windows, or similar
    openings
    (4) Where attached to building surfaces

    Bold by me.


  4. #4
    Join Date
    Jun 2008
    Location
    Maryland
    Posts
    1,097

    Default Re: radon fan wiring

    Quote Originally Posted by Rollie Meyers View Post
    Flexible cords are not allowed to pass through walls, doorways & such, here is a copy & paste from the 2008 NEC:

    400.8 Uses Not Permitted. Unless specifically permitted
    in 400.7, flexible cords and cables shall not be used for the
    following:
    (1) As a substitute for the fixed wiring of a structure
    (2) Where run through holes in walls, structural ceilings,
    suspended ceilings, dropped ceilings, or floors
    (3) Where run through doorways, windows, or similar
    openings
    (4) Where attached to building surfaces

    Bold by me.
    Thanks Rollie, that helps.