    Default Gas pipe through firebox

    Majestic fireplace has been upgraded to gas logs. Contractor installed copper gas pipe through base of unit instead of through side knockouts. Has this installation rendered this unit defective?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: Gas pipe through firebox

    Yes it is.

    Eric Barker, ACI
    Lake Barrington, IL

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Gas pipe through firebox

    Whoever installed the gas line damaged the protective metal liner and basically changed the design of the unit from what had been tested and approved by the manufacturer. I would direct them to a fireplace expert or qualified chimney sweep for additional information.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Default Re: Gas pipe through firebox

    The fireplace has a conduit on each side for a gas pipe penetration. This should be sealed at the inner metal firebox wall by packing around the gas pipe to the metal sidewall them again sealing around the pipe with refractory cement at the refractory panel. By making holes in the floor of the fireplace, heat could migrate into the lower compartment and out into the chase where it could cause an offset ignition or leak fumes into the home.

    That logset is way too big for that firebox. You should have 4-6 inches of free space to each side. The logset must be listed to ANSI Z21.60 or Z21.84 . Where is the shutoff and where is the control valve? Any more pics? Damper blocked wide open? Appears to have been operated with doors closed.

    Keep the fire in the fireplace.

  5. #5
    Join Date
    May 2009
    Location
    New Jersey
    Posts
    90

    Default Re: Gas pipe through firebox

    Bob,
    The damper block was present, however it was at the edge of the damper. This is where it is 99.5% of the time. I cannot find any documentation stating where it should be. Do you have anything?