04-28-2014, 01:17 PM #1
-
04-28-2014, 01:41 PM #2
Re: Jumpers across circuit breakers
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
04-28-2014, 02:00 PM #3
Re: Jumpers across circuit breakers
What Rick said or the feeders are not connected/not connected properly at the supply end and only one feeder is getting power.
If the feeders were both getting power that jumper would have melted and blown/burned away a long time ago.
My concern, above and beyond what is in those panels, is what is (more appropriately - what is NOT) in the panel where the feeders are connected to the supply.
-
04-28-2014, 02:47 PM #4
Re: Jumpers across circuit breakers
Walt I guess I did not refresh, but like the others here that would be in meltdown if it is from two legs. I assume it is a single leg and they are jumping over to the other side. So it must be all 120v.
Still wrong though
Last edited by Don Hester; 04-28-2014 at 02:50 PM. Reason: typo
Don Hester
NCW Home Inspections, LLC
Wa. St. Licensed H I #647, WSDA #80050, http://www.ncwhomeinspections.com
-
04-28-2014, 03:16 PM #5
Re: Jumpers across circuit breakers
Never thought to question if a meter has only one leg capped will it still run?
It looks like both panels for 1st and 2nd fl have breakers jumped.
So if one leg of meter is feeding the breaker they then jump to feed other leg side of panel.
-
04-28-2014, 03:22 PM #6
Re: Jumpers across circuit breakers
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.
-
04-29-2014, 05:39 AM #7
Re: Jumpers across circuit breakers
Didn't make any sense that it would make a difference. Thanks...