06-09-2014, 07:22 AM #1
Grounded conductor split between two terminals
Any real hazard associated with this?
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
06-09-2014, 07:45 AM #2
Re: Grounded conductor split between two terminals
Define "real" and "hazard".
Only when something goes not good ("wrong").
06-09-2014, 10:21 AM #3
The code requires the conductor to terminate in an individual hole. Lug adapters are available for larger,conductors.
06-10-2014, 08:55 PM #4
06-11-2014, 01:23 PM #5
Either leg could potentially carry the entire load of the full size wire. Since the leg is roughly half the size of the wire, it is undersized and could overheat leading to fire.
Is there a potential for arcs to jump between the two legs near where they split?
06-11-2014, 01:31 PM #6
The hazard would be if one were loose forcing the current onto the now undersized conductor. You could get some arcing at the loose connection to the bus.
06-23-2014, 10:22 AM #7
06-23-2014, 07:33 PM #8
That is a listing violation. The equipment label will state what size wire can be in the hole and that ain't it. Strands are broken and damaged.
06-24-2014, 12:02 AM #9