    Default Self Piercing Saddle Valves, Acceptable or Hack?

    Never been particularly happy with self piercing saddle valves but there are pretty common place for refrigerator ice makers, humidifers, and similar appliances.

    Are they code approved? If not, does anyone a reference that states they are contra-indicated?





    OREP Insurance
    "The Code is not a peak to reach but a foundation to build from."

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: Self Piercing Saddle Valves, Acceptable or Hack?

    As far as I know they are about as "code" approved as a flexible drain line on a kitchen or bathroom sink!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Atlanta, Georgia
    Posts
    1,088

    Default Re: Self Piercing Saddle Valves, Acceptable or Hack?

    Well the code at least states plumbing pipe must be smooth wall so actually contra-indicates corrugated flex pipe.

    I don't remember seeing anywhere that self piercing, self tapping valves are not allowed. Might be there, just can find it. Hoping someone could point to a specific reference. I can say I don't like them but that is not enough for me. I want an authoritive reference to confirm my dislike.

    "The Code is not a peak to reach but a foundation to build from."

  4. #4
    Join Date
    Mar 2007
    Location
    Charlotte, NC
    Posts
    112

    Default Re: Self Piercing Saddle Valves, Acceptable or Hack?

    Bruce....

    In the 2012 North Carolina Plumbing Code which is based on the 2009 Int'l Code, Section P605.9(4) lists "saddle-type fittings" as one of the prohibited joints and connections.

    Dave


  5. #5
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Self Piercing Saddle Valves, Acceptable or Hack?

    I've been out of town for a few days so was unable to reply.


    GA 2006 Plumbing code amendments (effective 1/1/2007)

    605.9 Prohibited joints and connections.
    4. Saddle-type fittings.
    Exception: Saddle-type fittings can be used to connect refrigerator ice makers to an existing
    residential unit water distribution system provided the manufacturer’s installation
    instructions for the distribution piping do not prohibit the use of saddle fittings. Saddle
    fittings can be used to install thermal expansion tanks to an existing residential unit water
    distribution system if approved by the manufacturer of the tank.
    (Effective January 1, 2007)

    Also of interest
    606.2 Location of shutoff valves.
    4. Shutoff valves to water supplies for refrigerators with automatic icemakers shall be accessible
    on the same floor as said refrigerators.
    (Effective January 1, 2007)

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  6. #6
    Join Date
    Dec 2007
    Location
    Holladay, UT
    Posts
    577

    Default Re: Self Piercing Saddle Valves, Acceptable or Hack?

    In my opinion these things are junk. In my area they are used a lot to supply water to evaporative coolers. They have to be turned off and water drained from the supply line every fall. I can tell you that a large per cent of them fail. They are fine as long as you don't operate them. I had heard that they were not allowed in some areas and I agree that they should not be allowed. They are the lazy way out. Have a qualified plumber install a proper brass ball shut off valve. JMO!!