Results 1 to 5 of 5
Thread: water heater ventilation
-
09-20-2014, 09:49 AM #1
-
09-20-2014, 11:13 AM #2
Re: water heater ventilation
A few"ifs":
- If the venting is natural drafting the minimum vertical rise measured from the vent draft hood bottom to the outlet of the gas vent must be not less than 5 feet.
- If the above is correct, the maximum horizontal offset must be no more than 75% of the vertical height (I recall some condition allows for a maximum of 100% horizontal offset).
- And, last but not least, probably should be first, a minimum rise of 12" before any horizontal offset starts.
- And other requirements apply as well.
-
09-20-2014, 12:36 PM #3
Re: water heater ventilation
JP gave the rules for venting a natural drafting gas water heater.
The other 2 possibilities are power vented and direct vented. Those can certainly be vented out thru the wall.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
09-20-2014, 01:53 PM #4
Re: water heater ventilation
Try to remember to collect as much data (and a few photos) as possible when you encounter an unfamiliar installation. Often times a quick web search of the make/model will reveal the installation details or instructions, and that can answer your questions quickly.
Dom.
-
09-21-2014, 11:32 AM #5
Re: water heater ventilation
Thank you, your expertise is much appreciated. I will provide more details and photos next time.