Double tapped?
I am a little rusty on double tapping. Is that when two conductors are under the same lug on one breaker that is not rated for double tapping?
double tapped.JPG
I am sure this guy was trying to break a record.
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-04-2015, 11:22 AM #2
Re: Double tapped?
It's when two wires are under any lug. As for as being acceptable it depends upon the rating of the equipment. Sometimes you can solve double tapped breakers with tandems but again it depends on what the panel is rated for. Worse case scenario will be the installation of a new panel or subpanel - let the electrician make that decision.
Eric Barker, ACI
Lake Barrington, IL
-
02-04-2015, 11:52 AM #3
Re: Double tapped?
The only manufacturer I am aware of is Square D, their breakers are approved for double taps, provided of course the wires being placed under the terminal are the same gauge
-
02-04-2015, 01:29 PM #4
Re: Double tapped?
It is Square D and Cutler Hammer (CH) breakers can be double-tapped. And not the really old breakers from either manufacturer.
Sometimes an electrician can just splice a pigtail on the two ends to repair. That depends on the loads expected on those 2 circuits.
If an old 70's panel has one double tap, in my area, it is likely to be a doorbell ringer, low voltage transformer, double-tapped on a 15 amp breaker in the old panel, was permitted, probably is a non-issue in that case.
But I look to see the transformer close by, not on the end of a long feeder that might have outlets and fixtures added.
Last edited by John Kogel; 02-04-2015 at 01:36 PM.
John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
02-04-2015, 01:47 PM #5
Re: Double tapped?
Door bell wire is stranded. Have seen double taps - solid wire and door bell stranded wire - the stranded wire is never under the terminal screw at least in my findings.
-
02-04-2015, 02:42 PM #6
-
02-04-2015, 02:45 PM #7
Re: Double tapped?
I know what you say, Raymond. The AHJ permitted it, but the connection on the doorbell wiring could be poor and then the bell won't ring.

John Kogel, RHI, BC HI Lic #47455
www.allsafehome.ca
-
02-04-2015, 03:01 PM #8
Re: Double tapped?
Can you get these connectors state side?
Marrette 3-Pack Black Plastic Standard Wire Connectors | Lowe's Canada
I like to use these whenever I can.
-
02-04-2015, 03:03 PM #9
Re: Double tapped?
-
02-04-2015, 04:22 PM #10
Re: Double tapped?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-04-2015, 04:28 PM #11
Re: Double tapped?
Nope; I don't know everything and don't let on I do. Didn't know about Cutler Hammer being approved and not afraid to admit that.
-
02-04-2015, 04:30 PM #12
Re: Double tapped?
If I am not mistaken there are lugs designed for 2 conductors. This depends on the lug. Post #1 http://www.inspectionnews.net/home_i...main-lugs.html
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-04-2015, 04:36 PM #13
Re: Double tapped?
On Square D or Cutler Hammer breakers that allow double tapping, the washer under the nut will have 2 places for the conductor/wires.
Here is a link by the start tribune.
Double Tapped Circuit Breakers | The Home Inspector | StarTribune.com
double tap break wire washer.JPG
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-04-2015, 04:47 PM #14
Re: Double tapped?
Thanks Robert, for the photo.
Also referring to your link to HG Watson, I forgot what a boorish dweeb this guy was. I am glad he is gone where ever he went. Talk about a know it all.
-
02-04-2015, 05:01 PM #15
Re: Double tapped?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-04-2015, 07:09 PM #16
Re: Double tapped?
The photo looks like an old Square D panel. I have not seen enough of them to know whether they were rated for two conductors. I do have some old breakers in my garage from a panel that burned up.
-
02-04-2015, 07:52 PM #17
Re: Double tapped?
It's an old Taylor electric panel and Taylor main disconnect fuse switch.
I recommended replacing/updating the first point of service.
taylor 125 panel.JPG taylor fuse switch.JPG
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-05-2015, 07:16 AM #18
Re: Double tapped?
Even for panels that have breakers designed for two wires, it is not allowed by any AHJs around here. So, I occasionally see two circuits connected with a pig tail going off to the breaker to satisfy the local AHJ's requirement of one wire one breaker.
If you choose not to decide, you still have made a choice.
-
02-05-2015, 09:54 AM #19
-
02-05-2015, 10:34 AM #20
Re: Double tapped?
Believe what they are trying to convey is that if a breaker is not designed for two wires then the wires can be pigtailed together and then one wire used for the (single wire) breaker.
The number of wires(circuits) that are being protected by a breaker has nothing to do with the load that the two circuits produce. The load calculation is a separate determination factor and is factored against the breaker capability/rating.
It is interesting that the electrician was able to get so many wires in the box with out having it look like a rat nest.
-
02-05-2015, 05:32 PM #21
Re: Double tapped?
Your previous post stated "That depends on the loads expected on those 2 circuits." as an condition of " ... an electrician can just splice a pigtail on the two ends to repair." - separating a multiple tap to one conductor at the breaker to two conductors does not alter any that exist ... except for correcting the multiple tap.
Originally Posted by John Kogel
-
02-08-2015, 03:53 PM #22
-
02-08-2015, 04:37 PM #23
Re: Double tapped?
Last edited by ROBERT YOUNG; 02-13-2015 at 07:23 AM. Reason: KISS
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-08-2015, 05:42 PM #24
Re: Double tapped?
-
02-10-2015, 06:49 AM #25
Re: Double tapped?
I did a FPE panel in New Hampshire last summer that had 7 triple tapped breakers, 6 double tapped breakers and 2" drywall screws driven into bundles of wire that looked like spaghetti in a colander...you guess it, screws has damaged wire insulation. Had listing RE agent on site at the time look at it...she immediately called her electrician!!!

- - - Updated - - -
I did a FPE panel in New Hampshire last summer that had 7 triple tapped breakers, 6 double tapped breakers and 2" drywall screws driven into bundles of wire that looked like spaghetti in a colander...you guess it, screws has damaged wire insulation. Had listing RE agent on site at the time look at it...she immediately called her electrician!!!
- - - Updated - - -
I did a FPE panel in New Hampshire last summer that had 7 triple tapped breakers, 6 double tapped breakers and 2" drywall screws driven into bundles of wire that looked like spaghetti in a colander...you guess it, screws has damaged wire insulation. Had listing RE agent on site at the time look at it...she immediately called her electrician!!!
-
02-13-2015, 07:34 AM #26
Re: Double tapped?
funny when you come to think of it.
I had to chuckle yesterday.
As I inspected an older 1950's build I ran across a Square D QO Load Center.
I dismounted the dead front and low and behold, a double tapping on a compliant breaker.
I told the client about the thread colleagues.
Square D double tap breaker.JPG
I do not run into double tapping breakers often, but when I do its like greeting a solid and trusted old friend. I get a smile, mentally reminisce and move on.
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-13-2015, 10:36 AM #27
Re: Double tapped?
One thing I did not see addressed was the double-tapping on the neutral terminals. Can't do that either.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
02-13-2015, 05:52 PM #28
Re: Double tapped?
Robert,
Those breakers are not "double tapped" ... those breakers have one terminal on one side of the plate and another terminal on the other side of the plate - they just have "one screw" which holds the right and the left terminals closed when that "one screw" is tightened.
-
02-13-2015, 05:59 PM #29
Re: Double tapped?
Not that I am the word police, and not that I have not typed the same thing myself (I have, many times), but ...
... they "can" do that - we find it all the time
... they are just "not allowed" to do that.
I try to not say "assume" as that can be changed around ... instead I try to always say "presume" (unless I am saying that someone ELSE "assumed" something ...
... then I say it occasionally).
I also try to not say that they "can't" do something which I am looking at ... because they "did" do it - I am looking at it.
-
02-13-2015, 08:06 PM #30
Re: Double tapped?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-14-2015, 07:03 AM #31
Re: Double tapped?
And I didn't say you said they were wired wrong either.
You stated "I dismounted the dead front and low and behold, a double tapping on a compliant breaker.", and I simply stated that they are not "double tapped" and explained why that term was not applicable.
"double wire/conductors under one terminal"I do not run into these breakers that accept double wire/conductors under one terminal often.
The point of my post was - those breakers have "two" terminals ... one terminal for each permitted conductors.
-
02-14-2015, 11:31 AM #32
Re: Double tapped?
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
02-14-2015, 12:28 PM #33
Re: Double tapped?
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
02-14-2015, 02:14 PM #34
Re: Double tapped?
If you choose not to decide, you still have made a choice.
-
02-14-2015, 04:21 PM #35
Re: Double tapped?
I suspect that most, if not all, of us use common language instead of actual code language.
My post to Robert was not correcting or pointing out the use of common language should have been code language - it was that the common language of double tapped does not apply to a breaker which as two terminal together like Sq D has.
My post to Gunnar was, I thought, obviously humorous in and of itself in mentioning the fact that when we say "you can't do that" ... and we are standing there looking at it ... obviously ... they CAN do that ... they DONE DID IT ... but it just ain't right (I am allowed to use "DONE DID IT" and "ain't" here, right? )

-
02-15-2015, 07:38 AM #36
-
02-15-2015, 02:04 PM #37
-
02-15-2015, 02:09 PM #38
-
02-16-2015, 06:48 AM #39
Re: Double tapped?
Check the attachment out..
www.1stproinspection.com
Certified Master Inspector
Like Us On Facebook https://www.facebook.com/1stproinspection/
-
02-16-2015, 07:14 AM #40
Re: Double tapped?
Double tapped beer kegs are convenient at parties and legal in most states.
If you choose not to decide, you still have made a choice.
-
02-16-2015, 07:29 AM #41
Re: Double tapped?
Double tapping neutrals is a very common find in panels supposedly installed by licenced electricians. As a matter of fact its so common it tends to be more common then double taps under the terminal screws of the breaker.
-
02-16-2015, 07:23 PM #42
Re: Double tapped?
If these panels were installed under the 2002 or later NEC, the term is "licentious electricians." Possibly just due to ignorance.
vide NEC Section 408.41, formerly 408.21.
Note that the exception for circuits with parallel conductors concerns circuits that, to start with, require minimum 1 AWG size conductors.
If installed under an earlier NEC, here's what Jim Pauley, now I believe president of NFPA but then with Square D, said, in the substantiation of his proposal that brought this section into the 2002 and subsequent NEC (#9-113, Log#3287, should you want to look it up for yourself) : "This revision is needed to coordinate the installation requirements with a long standing product standard requirement. Clause 12.3.10 of UL 67 (Panelboards) . . . The requirement has been enforced in the past by a close review of the manufacturers markings . . . "
In other words, the instructions in every listed panelboard have said for decades that you can't put anything but a single neutral wire in its hole.
-
02-16-2015, 07:56 PM #43
Re: Double tapped?
Thats fine but its obvious many an electrician cannot read.In other words, the instructions in every listed panelboard have said for decades that you can't put anything but a single neutral wire in its hole.
- - - Updated - - -
Thats fine but its obvious many an electrician cannot read.In other words, the instructions in every listed panelboard have said for decades that you can't put anything but a single neutral wire in its hole.
-
02-17-2015, 06:53 AM #44
Re: Double tapped?
Agree.
Last year I butted heads with a long time electrician who corrected the double lugged neutrals by twisting them together and putting them back under the same lug. When I checked with the local AHJ to confirm that they didn't have a variance, he called the electrician an idiot. Because I'm a helpful kinda guy, I sent the electrician the attached illustration.
ground-neutral-terminalbars.jpg
If you choose not to decide, you still have made a choice.
-
02-17-2015, 12:38 PM #45
Re: Double tapped?
I have a different take - Although I understand the need to occationally double tap a breaker like a door bell. I would like to point out that this box may actually be over capacity in wires. Like conduit boxes actually have a maximum capacity - physically this one looks like it is there, but also to shead any heat load that may be occuring
- espcailly at the sweet 16 party your customer is going to have where the house is at full occupancy every TV , Xbox , hair dryer , oven , cloths dryer , hot tub - the band hooked up to what ever spare circuit they could find or what ever the occasion (of course this is where we find out that Joe the deck builder never did any load calculations and we find out that the deck can not hold 50 of your heavest friends either
-
02-17-2015, 12:59 PM #46
Re: Double tapped?
I have a different take - Although I understand the need to occationally double tap a breaker like a door bell. I would like to point out that this box may actually be over capacity in wires. Like conduit boxes actually have a maximum capacity - physically this one looks like it is there, but also to shead any heat load that may be occuring
- espcailly at the sweet 16 party your customer is going to have where the house is at full occupancy every TV , Xbox , hair dryer , oven , cloths dryer , hot tub - the band hooked up to what ever spare circuit they could find or what ever the occasion (of course this is where we find out that Joe the deck builder never did any load calculations and we find out that the deck can not hold 50 of your heavest friends either
-
02-17-2015, 01:43 PM #47
Re: Double tapped?
Over loading a circuit is definitely a consideration with double tapped breakers. It's the reason most often stated by most of the AHJs around here why they don't allow two wires on a Square D breaker that is designed to accept two wires. Yet, I occasionally see two circuits under a wire nut with the pig tail going to a breaker to satisfy the one wire per breaker requirement.
Most of the time, it's very difficult for us to determine if a circuit is over loaded. A few weeks ago, a renter disclosed that whenever his wife was running a kitchen counter appliance while he was running a tool in the garage, the breaker (with only one wire to it) would trip. I wrote it up.
If you choose not to decide, you still have made a choice.
-
02-17-2015, 06:21 PM #48
Re: Double tapped?



Reply With Quote