Results 1 to 4 of 4
  1. #1

    Default CSST bonded to black iron pipe

    Is CSST considered bonded if it is an extension of the existing black iron gas piping system or must it be separately bonded?

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: CSST bonded to black iron pipe

    Quote Originally Posted by Don Hawley View Post
    Is CSST considered bonded if it is an extension of the existing black iron gas piping system or must it be separately bonded?
    To my understanding, ALL CSST is required to be bonded with a bonding jumper to the GEC system with the appropriate heavy copper wire and clamp attached to the black iron pipe, etc. (not the CSST itself)
    incidental bonding through the equipment ground of attached systems is not enough.
    A foot or a mile triggers the same requirement.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: CSST bonded to black iron pipe

    Quote Originally Posted by Don Hawley View Post
    Is CSST considered bonded if it is an extension of the existing black iron gas piping system or must it be separately bonded?
    This spells it out pretty good.
    http://www.csstsafety.com/Images/CSS...h-Bulletin.pdf

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: CSST bonded to black iron pipe

    This addresses bonding of CSST: http://jerrypeck.com/IFCN/2015-11%20...-11%20IFCN.pdf

    The code reference is the Florida Building Code, but it is likely the same as or similar to the code for your area as the Florida codes are based on the ICC codes.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •