Results 1 to 20 of 20
    Default AFCI Outlet Device
    Hi folks,
    New construction, not occupied. There was one AFCI breaker in the garage panel. There were a few other outlet-type AFCI devices protecting receptacle outlets in the interior. Lights were not protected as far as I could determine.
    My understanding is that AFCI protection is required at the panel, unless the cable between the panel and the first outlet device is RMC, IMC, EMT, MC or AC; or embedded in concrete (CEC Article 210.12 A Exception 1). Also, ALL outlets (light, smokes, receptacle outlets, etc.) are required to be AFCI protected.
    I haven't run into AFCI outlets before, so I was unsure. Do I have it right?
    Default Re: AFCI Outlet Device
    The lights are required to be AFCI protected. What NEC edition does CA use? 2011? 2014?
    The 2014 NEC makes it a lot more complicated. I didn't put all those complications in my AFCI list as it would take up half a page.
    Hi Jerry,
    Thanks. Pretty much what I thought.
    CA uses the 2013 California Electric Code which is based on the 2011 NEC. Next update is 2016 which will incorporate the 2013 NEC.
    Great. Maybe I will retire before then. Fortunately, I mostly inspect existing buildings, so it will be a while before I start seeing 2014 requirements. Is this on your website for free download by ME???
    Kevin,
    Not a code inspection. Pre-sale. Nonetheless, I try to get things right. BTW, no AFCI redundancy that I could find. I couldn't figure out what the one AFCI breaker in the panel did. Tripped it and couldn't find any protected circuits.
    Gunnar,
    Inspectors
    Just for you ... no one else can see them ... bottom of the electrical column - oh, wait, that just let everyone else know where to look ... OH DARN!
    Want me to add you to my newsletter email list so I send them to you when I send them out? Just let me know, PM, email, or post it here ... same for everyone else, just let me know - send me your email address.
    Last edited by Jerry Peck; 10-13-2015 at 06:53 PM. Reason: added part about signing up for newsletter
    Cool Re: AFCI Outlet Device
    Wow, derating and all kinds of other nifty stuff! You shouldn't give this stuff out for free.
    Ummm... forget I said that.
    Jul 2012
    north carolina
    Gunnar,
    Inspectors
    Mr Peck- I would appreciate anything you send out- jdpavan@gmail.com
    Quote Originally Posted by JOHN PAVAN View Post
    John,
    I've added you to my email list, thank you.
    Previous newsletters can be read/downloaded here: http://jerrypeck.com/IFCN/IFCN.htm
    Jul 2012
    north carolina
    John,
    GREAT. I really appreciate your willingness to share the depth of knowledge you possess.
    Chandler, AZ
    John,
    Jerry, please add me too. Cheers!
    Dave
    BuyersSellersPi@aol.com
    Dave Hill
    Buyers & Sellers Property Inspections LLC
    WWW.BuyersSellersPi.Com
    I would appreciate being added to your email list for this.
    tim@nittygrittyinspections.com
    Thank You!
    Tim Kaiser
    Gunnar,
    Inspectors
    Dec 2013
    United States
    Please add me to your mailing list, great information.
    Bill.atchley@gmail.com
    Quote Originally Posted by Dave Hill View Post
    Dave
    Dave,
    I will add you to my newsletter mailing list when I get back to my office.
    Thank you.
    Hi folks,
    Please check for the AHJ electrical buyoff label that should be affixed on the premises equipment or contact the local building department to find out what the electrical code adoption is compliant to in the area. The Cali State requirements do not comply totally within the 2014 NEC code cycle.
    Your interpretation of the latest NEC may be correct but some local AHJ's overrule or add various AFCI usage requirements. Make your report stating that there must be approved labeling indicating the electrical wiring has been AHJ certified for the new construction compliance. Let the local code directives carry the liability...by a qualified AHJ electrical inspector.
    Oct 2014
    Hi folks,
    Jerry's right about the lights.
    As for the complicated requirements, 2014's 210.12(A)(4) simplifies things, in that even with new wiring you don't need the (nobody makes one) supplemental arc protection circuit breaker so long as the AFCI device is within 50-70 ft of the CB, depending on gage, measured along the cable. Whether the AHJ would accept compliance with a later version of the NEC is uncertain but possible. But this is irrelevant if the lighting is on a different circuit. Still and all, so long as certain mistakes are absent, correcting this is not a big deal.
    Dave
    Dave,
    I've added you to the email distribution list too.
    Thank you,
    Jerry
    Nov 2010
    Safety Harbor, FL
    Gunnar,
    Inspectors
    Would like for you to add me to your newsletter subscriber list. Thanks!
    onthegulf1@me.com
    Quote Originally Posted by Bob Wisnewski View Post
    onthegulf1@me.com
    Bob,
    I've added you to my newsletter distribution email list.
    Thank you,
    Jerry
    Oct 2011
    california
    Bob,
    Thank you,
    Jerry
    If you have a news letter which will supply me with any needed information useful to my inspection construction business please add me
    Frazier
    Bob,
    Thank you,
    Jerry
    Frazier
    Bob,
    Thank you,
    Jerry
    Frazier
    Quote Originally Posted by frazier jeffery View Post
    Frazier
    Frazier,
    I don't know if you need the information or not ... ... send me a PM with your email address and I will add you to my newsletter distribution list.
    Thank you,
    Jerry
    Hi David,
    Are you the David E. Shapiro, author of YOUR OLD WIRING? If so, I think this book would be an excellent reference to home inspectors who have the need to inspect existing homes with wiring deteriorated conditions.
    Dave, I can help you update your book next edition run with the latest in electrical installation advanced dwelling wiring methods such as clean NM bundling with Dual Function technology and individual wiring termination techniques. PM email if interested. Ben
Tags for this Thread
