    Default outlet tester results

    If an out let tests out to having only 89 volts going to it, 1) would a three prong tester show "ok" or 2) would it show unpowered?

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Nov 2010
    Location
    New Westminster BC
    Posts
    55

    Default Re: outlet tester results

    Quote Originally Posted by Norm Peery View Post
    If an out let tests out to having only 89 volts going to it, 1) would a three prong tester show "ok" or 2) would it show unpowered?
    Don't know if there's one answer for all makes of testers, but the Marr 0808 and Klein RT100 receptacle testers have small neon bulbs in them. These kinds of neon bulbs are specified to light up by the time the voltage gets up to 90 volts, so probably work on 89 volts.

    A greater concern should be the low voltage itself, suggesting that the current is too high for the length and gauge of the conductors feeding the loads. If 89 volts "going to it" means 89 volts at the outlet with no load on the outlet, then other loads and the upstream cables are mismatched, plus if you then draw power from the outlet the voltage will drop even below 89 volts.

    What is the voltage at the service entrance? - more than 94 volts means the max voltage drop of 5% from service to point of use is being exceeded, not allowed by most electrical codes. If the supply is less than 94 volts then the problem is outside with the utility, or maybe too many high current grow-ops in neighbouring houses.


  3. #3
    Join Date
    May 2011
    Location
    Clarkesville, Georgia
    Posts
    41

    Default Re: outlet tester results

    If you are using a digital meter, there is a good chance that there is not 89 volts, adding load or using solonoid tester may make voltage drop to zero. The neon tester may be enough of a load to do this, or may glow dim.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: outlet tester results

    If you measure anything outside the 120-125 volts +/- 5 volts or so, there is a good possibility that there is a problem with the neutral (or poor meter connection at plug-in fittings).

    If the neutral is solidly (good connection) grounded and the meter connections are good, the voltage should be the same on both legs (bus bars) and measure the same at all receptacles.

    At 90 volts on one leg, there would be 150 volts on the receptacles on the other leg (90 + 150 = 240) as there will be 240 volts +/- to the service.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •