Results 1 to 8 of 8
  1. #1
    Join Date
    Mar 2007
    Location
    NoCal
    Posts
    261

    Default 60 or 90 - choose

    Main panel was a 200 amp, with a 2-pole sub-feed to the interior panel, SFD.
    The 2-pole sub-feed breaker was 1/2 60 amp and 1/2 90 amp.
    Mis-matched circuit breaker amperages was a 1st for me. I reported as needing correction...but what are the implications of use or safety?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 60 or 90 - choose

    What was the rating of the mains (bus) for the remote interior panel?
    What were the ratings of the feeder conductors ('hot' and 'neutral' conductors)?

    Both of all of the above should be at least the 90 amps of the larger breaker.

    With one breaker being a 60 amp and one being a 90 amp, it is possible that the panel is balanced to put 30 amp on what would normally be the 'neutral' conductors, but, if this was done, it would no longer be a 'neutral', it would just be a 'grounded' conductor.

    And, yes, as you suspected ... that ain't right and needs to be fixed.

    Hopefully someone did that because they only had on 90 amp single pole breaker and one 60 amp single pole breaker on/in their truck/tool box and 'forgot' to come back and replace the 60 amp breaker with another 90 amp breaker.

    Hopefully someone did NOT do the opposite and intend on the 90 amp being on a 60 amp rated panel or conductor ... hopefully ...

    Maybe someone was dyslexic and thought they were both 90 amp breakers?

    There were single pole breakers and not a manufactured made-together-double pole breaker, right?

    If it was a made together double pole breaker, the factory needs to know and replace it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    NoCal
    Posts
    261

    Default Re: 60 or 90 - choose

    If it was a made together double pole breaker, the factory needs to know and replace it.

    Yes, it appears to be a factory made breaker. Its' weird, Harold!


  4. #4
    Join Date
    May 2008
    Location
    N. Syracuse, NY
    Posts
    36

    Default Re: 60 or 90 - choose

    That's a factory installed handle tie. As far as I know, there are no single pole 60 or single pole 90 amp breakers. Why would there be? Finally, the lugs appear to be the same size. If the ratings actually corresponded to the overcurrent protection, the lugs would be different sizes. That's a DP 60A Eaton breaker with a typo.


  5. #5
    Join Date
    Mar 2007
    Location
    NoCal
    Posts
    261

    Default Re: 60 or 90 - choose

    Quote Originally Posted by Mike Locurcio View Post
    That's a factory installed handle tie. As far as I know, there are no single pole 60 or single pole 90 amp breakers. Why would there be? Finally, the lugs appear to be the same size. If the ratings actually corresponded to the overcurrent protection, the lugs would be different sizes. That's a DP 60A Eaton breaker with a typo.
    I follow the logic that it's a factory 2-pole, Mike. It must be a typo, right????? or??? do we take a magic marker to the thing to fix it? My vote is to replace it with one with proper labeling and markings to avoid confusion.


  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: 60 or 90 - choose

    Quote Originally Posted by Mike Locurcio View Post
    That's a DP 60A Eaton breaker with a typo.
    Or is it a 90 amp breaker with a typo? (wrong handle installed)

    Or is it really a 60 amp and a 90 amp put together by mistake?

    I vote for the latter ...

    ... because if we presume that it is a 'typo' (wrong handle installed on the breaker) ... then how many '60' amp breakers are really '90' amp breakers with the wrong handles, and vice versa.

    I would much rather presume that each breaker (half the double) is correctly made, and that two mismatched breakers were inadvertently assembled together.

    Regardless, and as I said, the factory needs to know and replace the breaker.

    They need to know so they can figure out what is what and what and why that happened.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Oct 2013
    Location
    United States
    Posts
    11

    Default Re: 60 or 90 - choose

    Appears to be two single pole breakers with a common trip added.


  8. #8
    Join Date
    Oct 2014
    Location
    Maryland, DC, and Northern Virginia, electrical only
    Posts
    460

    Default Re: 60 or 90 - choose

    Quote Originally Posted by Jerry Peck View Post
    Or is it a 90 amp breaker with a typo? (wrong handle installed)

    Regardless, and as I said, the factory needs to know and replace the breaker.

    They need to know so they can figure out what is what and what and why that happened.
    Most certainly. It also seems questionable whether they would trip together. Handle ties only ensure that you can't through one without throwing the other, not the same as having an internal common tripping mechanism.

    It would be interesting for the purchaser to know whether the jurisdiction has a re cord of a permit and a passed inspection covering the subpanel installation, presuming that there is a jurisdiction requiring permits and inspection. If so, it still doesn't make this installation right; if not, one can readily question the suitability of relying on the feeder, not just on its overcurrent protection.


Tags for this Thread