Results 1 to 7 of 7
Thread: Generator lock out switch.
-
05-11-2017, 07:49 AM #1
Generator lock out switch.
I saw this lock out switch for generator back feed connection.
Are these code approved?
Similar Threads:
-
05-11-2017, 11:56 AM #2
Re: Generator lock out switch.
Looks like a factory breaker interlock. Was the breaker retention device in place on the generator breaker?
All answers based on unamended National Electrical codes.
-
05-11-2017, 12:13 PM #3
Re: Generator lock out switch.
Maybe I'm not seeing the photo right, but I don't see where that prevents both being on at the same time.
Am I just not seeing it?
-
05-11-2017, 01:00 PM #4
Re: Generator lock out switch.
I went back and zoomed in on the photo on my computer (I was looking on my phone earlier) and then I could see where raising the lockout up is blocked by the breaker when the main utility power breaker is 'on', and when the main utility power breaker is turned off - the lockout can slide up, which allows the generator breaker to be turned 'on'.
Hope those screws on the left are not very long ...
-
05-11-2017, 02:00 PM #5
Re: Generator lock out switch.
Normally just long enough to get a nut on the inside to hold the bracket.
All answers based on unamended National Electrical codes.
-
05-26-2017, 12:02 PM #6
Re: Generator lock out switch.
-
05-26-2017, 12:50 PM #7
Re: Generator lock out switch.



Reply With Quote