Results 1 to 25 of 25
Thread: Two panels from the meter
-
06-05-2019, 04:01 PM #1
Two panels from the meter
Not sure about this. First time I have ever seen it; 2 panels directly from the meter, one in the house and one in the garage. Can't upload photos for some reason. There are 2 cables that come from the meter, to 2 different main panels. On come from the bottom into the home, the other from the side, underground to the garage.
Similar Threads:
-
06-05-2019, 05:13 PM #2
Re: Two panels from the meter
First, drop the use of the term "main panel" and start using the term "service equipment" (which includes the "main service disconnect").
From your description of location, the service equipment panel would be, should be, the panel outside at the meter.
However, you also said that both panels were "directly from the meter", which is not allowed when one panel is outside and the other panel is inside.
So, based on your description ... the only thing we can say is "one or both of the panels are not wired properly".
Photos may help expand on that statement, or maybe confirm the statement, and maybe even add to the statement.
-
06-05-2019, 05:34 PM #3
Re: Two panels from the meter
Ok, Jerry, one service panel is inside the house, and one is inside the garage the garage. They both come directly off the meter pan. There is a distribution panel on the second floor that is fed from the service panel in the home, which is not properly wired. I have never seen 2 service panels from one meter. I don't know why I can't download a frick frackin picture. I just sent the picture to your personal email.
-
06-05-2019, 06:01 PM #4
Re: Two panels from the meter
Russel,
It's been 20 minutes and no photos have arrived yet, nonetheless ...
From my first reply, and from your description above:
That is not allowed, as previously stated.one service panel is inside the house, and one is inside the garage the garage. They both come directly off the meter pan.
Which means that ONE of them (the best one would be the outdoor panel) needs to be made into THE service equipment panel, and that panel then feeds the other panel, OR ... or either panel can be relocated to where the other panel is so that BOTH service equipment panels are next to each other (grouped together) either inside or outside.
Depends on if the capacity of BOTH of the panels is needed (move the panels to be grouped together) or if the capacity of ONE panel (the larger of the two panels if they are not the same rating) is suitable for the entire house (make the larger rated panel THE service equipment panel) then rewire as needed to make end result correct.
-
06-05-2019, 06:55 PM #5
Re: Two panels from the meter
The meter could feed into the service panel for the house and a disconnect for the garage to satisfy the.grouping requirement.
All answers based on unamended National Electrical codes.
-
06-05-2019, 07:20 PM #6
Re: Two panels from the meter
"satisfy the.grouping requirement"
With one disconnect outside and one disconnect inside?
No place that I've even been would consider an outside and inside disconnect as being "grouped".
Granted, I haven't been that many places, but just yesterday I was talking with an electrical contractor from California and he brought that very issue of grouping up, and not there either.
Disconnecting means. A device, or group of devices, or other means by which the conductors of a circuit can be disconnected from their source of supply.
https://www.merriam-webster.com/dictionary/group
(sorry for the strange font sizes, it was a copy and past from the website)
group
noun, often attributive
\ ˈgr?p
\
Definition of group
(Entry 1 of 2)
1: two or more figures forming a complete unit in a compositionwent there as a group
2a: a number of individuals assembled together or having some unifying relationshipa study group
b: an assemblage of objects regarded as a unitone of the food groups
c(1): a military unit consisting of a headquarters and attached battalions
(2): a unit of the U.S. Air Force higher than a squadron and lower than a wing
3a: an assemblage of related organisms ?often used to avoid taxonomic connotations when the kind or degree of relationship is not clearly defined
b(1): two or more atoms joined together or sometimes a single atom forming part of a moleculeespecially : FUNCTIONAL GROUPa methyl group
(2): an assemblage of elements forming one of the vertical columns of the periodic table
c: a bed or layer of rocks deposited during an era
4: a mathematical set that is closed under a binary associative operation, contains an identity element, and has an inverse for every element
This part best describes and applies to a group of disconnects:
2a: a number of individuals assembled together or having some unifying relationshipa study group
b: an assemblage of objects regarded as a unitone of the food groups
-
06-05-2019, 10:52 PM #7
-
06-05-2019, 11:33 PM #8
Re: Two panels from the meter
It's the need to know you've killed all power. It's similar to the concept that's driven the move in the last two Code change attempts to have an outside service disconnect or group of disconnects, so firefighters eventually can know before entering the home, and without yanking the meter, that they have a way to ensure their electrical safety however and wherever they get in a building. It's also why you note the location of other sources of energy.
-
06-06-2019, 03:13 AM #9
Re: Two panels from the meter
I was thinking generator equipment myself.
Two panels from the meter is not an issue hypothetically. As long as the cables are connected properly, equipment is recent, no obsolete, and the meter can read how much power was used so POCO can bill the civic address occupants.
Last edited by ROBERT YOUNG; 06-12-2019 at 04:16 AM.
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
06-06-2019, 04:21 AM #10
Re: Two panels from the meter
This was a common way to wire houses with electric heat back in the 60es here in New England , The panels would be side by side and one panel would have all the heat in it.
-
06-06-2019, 05:17 AM #11
Re: Two panels from the meter
I sent the picture to Jerry via his email. maybe he will post it.
I sent the report to my client last night calling it out as "not allowed". Hope that wasn't a mistake.
Still can't figure out why I can't post pictures. It is not too big, file name is ok. Just wondering if I have too many pictures already loaded, but I can't figure out how to delete the old pics. Jeeze.
-
06-06-2019, 11:08 AM #12
Re: Two panels from the meter
This is exactly what I have to get power to my garage , shop. I have a 400amp meter base that has a built in disconnect and two sets of lugs, one set for the 200amp panel in the house and one for the 200amp panel in the garage. I had to run a 500 mcm service entry cable to the meter base then a piece of 4/0 use to the house panel, to the garage is 3 inch conduit with 3 4/0 cables and one #4 safety ground that runs underground for 75 feet and terminates at the panel inside the garage. I also had to drive 2 8ft ground rods for earth grounds at the meter base and one 8ft ground rod at the garage these were all bonded to the panels and meter base. Power company did upgrade for nothing and it saved me about $4000 for what the power company was going to charge for running to the garage with a separate service.
-
06-06-2019, 11:14 AM #13
Re: Two panels from the meter
This is exactly what I have to get power to my garage , shop. I have a 400amp meter base that has a built in disconnect and two sets of lugs, one set for the 200amp panel in the house and one for the 200amp panel in the garage. I had to run a 500 mcm service entry cable to the meter base then a piece of 4/0 use to the house panel, to the garage is 3 inch conduit with 3 4/0 cables and one #4 safety ground that runs underground for 75 feet and terminates at the panel inside the garage. I also had to drive 2 8ft ground rods for earth grounds at the meter base and one 8ft ground rod at the garage these were all bonded to the panels and meter base. Power company did upgrade for nothing and it saved me about $4000 for what the power company was going to charge for running to the garage with a separate service.
-
06-06-2019, 12:04 PM #14
Re: Two panels from the meter
-
06-09-2019, 09:56 AM #15
Re: Two panels from the meter
IMG_0182.JPG
Yesterday's Home on Puget Sound, Place was only 2500Sqft but had three additions - 2 Attics, Two Water Heaters, Two Panels, and 4 Crawlspaces - I definitely underbid it !
Last edited by Jim Hintz; 06-09-2019 at 10:05 AM.
-
06-09-2019, 10:45 AM #16
Re: Two panels from the meter
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
06-09-2019, 10:48 AM #17
Re: Two panels from the meter
Part of the 2500 sq ft or in addition to the 2500 sq ft? If in addition too, then the price goes up as the client mis-represented what you were going to inspect. If part of the 2500 sq ft ... how small was the house originally - but it doesn't matter as the correct sq ft was given.
Not uncommon from my experience, not even the 4 crawlspaces (for houses which had crawlspaces, fortunately, most of my inspections were were slab on grade); multiple attics (access multiple areas) was common.Two Water Heaters, Two Panels, and 4 Crawlspaces - I definitely underbid it !
However, the reason I was replying is that in the photo, there are two equal sized raceways going up into the meter can - not two sets of service entrance conductors (conductors in parallel) are there, and not from two sources are they (one from an optional standby generator)?
Curious as to why two conduits for service entrance conductors.
-
06-09-2019, 07:24 PM #18
Re: Two panels from the meter
Well in Georgia, we have houses that are wired, and in My county was allowed to have two panels off the one meter, mostly in homes that had 400 amp service, two 200 amp panels side by side with their own disconnect bot wired back to the meter
-
06-10-2019, 09:13 AM #19
Re: Two panels from the meter
Hi Jerry,
No generator setup. Place used to be a "Cabin" decades ago and was added onto, remodeled, etc...The reason there were 4 crawlspaces was you have to go through a hole blasted through a foundation wall to get under an added portion of the structure. Each panel controlled circuits for particular rooms in the residence. Each panel was bonded also.
- - - Updated - - -
My pricing is based on square footage and year built. I also have access to the MLS. 99.999% of the time there is nothing mentioned about additions / multiple attics, crawlspaces, service panel, etc., in the Client or Agent remarks concerning the Listing.
-
06-12-2019, 12:38 AM #20
-
06-12-2019, 04:24 AM #21
Re: Two panels from the meter
Morning, Jerry. Hope to find you well and in good spirits and heath this lovely day.

Not saying anything negative about the information you posted.
but I find Swiping and Pasting material from other internet site to InspectionNews MB threads leaves a little bit to be desired. I typically/usually use Word to translate articles I find/found on the internet to InspectionNews MB.
Hope that helps
Robert Young's Montreal Home Inspection Services Inc.
Call (514) 489-1887 or (514) 441-3732
Our Motto; Putting information where you need it most, "In your hands.”
-
06-12-2019, 04:34 AM #22
Re: Two panels from the meter
HOWEVER ...
There are two photos below in recent posts which show: one is definitely not done properly (one disconnect outside and one disconnect inside); the other has an unanswered question (why two conduits going to the meter).
Why we say "if done properly this" ... we need to be clear what "this" is, so we don't give a false impression of what is being referred to.
And, yes, I saw the quote being replied to, but are you saying that it has to be done "that way" to be right?
-
06-12-2019, 04:48 AM #23
Re: Two panels from the meter
Robert,
Curious why you think copy and paste leaves a bit to be desired (what you called "Swiping and Pasting").
I provided the source, the link, and highlighted the applicable part.
To me, that's better than swiping someone else's work, editing it, and posting "your version" of it to explain something or define something.
Posting information by others and acknowledging the source is something we do all the time.
Have you ever referenced a code, standard, or some other source, the posted that information here? (No need to answer, we've all seen you do it. Are you now saying it's not good to acknowledge the source of the information, and that we should edit it to look like our information?)
-
08-08-2019, 09:25 PM #24
Re: Two panels from the meter
Good choice Richard! After they had charged you the $4000 for the second service most of the POCOs which I have dealt with would have charged you $20 a month for reading a second meter for a single customer. The wonder is that the utility regulators still let them do that when they now have smart meters which do not even need a meter reader.
--
Tom Horne
-
08-09-2019, 05:44 AM #25



Reply With Quote

Bookmarks