Results 1 to 4 of 4
-
04-01-2020, 03:01 PM #1
Flue Pipe on this Gas Water Heater
I don't think this would be acceptable, because there is no 90 degree turn on the flue pipe coming up from the water heater ?
Similar Threads:
-
04-01-2020, 06:49 PM #2
Re: Flue Pipe on this Gas Water Heater
Sam,
I am unsure as to why you even used a question mark at the end of that sentence. I halfway believe that you posted this as an April Fools prank.
Tape is not acceptable.
Requires a fitting of some kind.
Doesn't look like the single-walled flue pipe has screws.
Looks like the large gas vent pipe is sloped the wrong way.
No. Not acceptable.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
04-07-2020, 07:20 PM #3
Re: Flue Pipe on this Gas Water Heater
Agree all points as usual Gunnar. Also, if you look it up in the sizing charts at less than 3 feet vent rise, must be 4" vent connector. If this goes to a listed liner then wall shield ok. If not, need cleanout within 12" but then again, I've never found a heater flue that didn't need a liner.