Foundation consists of two different sized block walls.
The foundation consists of two different sized block walls. The right angle area at the offset does not have mortar filled in. Anyone have a code reference I can paraphrase? Also, what do you say about it?234-1.JPG
Similar Threads:
-
01-17-2020, 07:09 AM #2
Re: Foundation consists of two different sized block walls.
Is that a short CMU wall on top of an un-grouted stem wall?
On top of a footing, I imagine? Any reinforcement steel visible?
-
01-17-2020, 01:47 PM #3
Re: Foundation consists of two different sized block walls.
From ACI 530 (I don't recall the section number): face shells shall be fully bedded.
The reason is that the load on concrete block walls is carried down through the face shells, thus the face shells are required to be fully bedded in the mortar bed ... which is no possible when there is no mortar bed under the face shells going across the open cells below. Which means that the course below needs to be fully grouted, and quite likely, that fully grouted is for the two courses below it (I am basing that two courses below being fully grouted on the fact that when the face shells overhang the edge of a slab, the engineered fix is always to fully grout the two bottom courses of the wall which is resting on the slab but overhanging the slab - there must be a reason why that is what all of the engineers have designed when that arises).
-
01-18-2020, 07:33 AM #4
Re: Foundation consists of two different sized block walls.
If you choose not to decide, you still have made a choice.
-
01-18-2020, 12:08 PM #5
Re: Foundation consists of two different sized block walls.
The photo shows that the face shells of the smaller blocks of the upper course are set in mortar on the webs of the larger blocks of the lower course.
The requirement is that the face shells shall be fully bedded.
The only way to fully bed the face shells of the smaller blocks of the upper course is to fill the cells of the larger blocks of the lower course to that that face shells of the upper blocks are fully bedded (set in full bed of mortar) on the filled cells of the lower course ... not just set in mortar on the webs of the lower course.
Zoom in on the photo and you can see the light and shadows going down into the hollow cells of the lower course, you will also see the hollow/empty space between the upper course and the lower course where the mortar would be if the face shells were fully bedded.
The wall constructed of larger blocks on the footing, and with smaller blocks offset from center (exterior face shells aligned, which appears to be the case in the photo), creates an eccentrically loaded footing ... which is not good ... unless the footing was designed for the eccentric load (such as making the footing wider to the side of the wall where the smaller blocks have their face shells aligned with the face shells of the larger block below - but that footing would not be visible or known to the inspector unless the inspector was doing a different type of inspection and digging out the other side of the footing to determine is size and depth ... and that should be left to the engineer to do who is documenting that the footing was designed for the eccentric load).
Last edited by Jerry Peck; 01-18-2020 at 12:14 PM. Reason: speelin'
-
01-19-2020, 06:43 AM #6
Re: Foundation consists of two different sized block walls.
Peter,
See page 1 of attached.
https://www.nj.gov/dca/divisions/cod...C_Smr_2019.pdf
Darren www.aboutthehouseinspections.com
'Whizzing & pasting & pooting through the day (Ronnie helping Kenny helping burn his poots away!) (FZ)
-
01-29-2020, 07:38 AM #7
Re: Foundation consists of two different sized block walls.
Are there any signs of structural defects? From a home inspection stand point, is this truly a defect needed to be reported with recommendation for repairs?
-
01-29-2020, 10:10 AM #8
Re: Foundation consists of two different sized block walls.
That IS "A structural defect" ... unless one only considers it a structural defect after it has fallen ... in which case it may also be a criminal defect for causing injuries/deaths.
That's what home inspectors are hired for - to advise their clients of things like that.From a home inspection stand point, is this truly a defect needed to be reported with recommendation for repairs?
-
01-29-2020, 10:55 AM #9
Re: Foundation consists of two different sized block walls.
Questions I would ask are: How old is the house, how many stories, are windows/doors out of plumb, is there any walls / ceilings with major cracks? Is there current foundation damage? These are all indications if the system isn't functional. Is this typical construction for the area?
In my area I rarely see CMU blocks. When I do its full basements so this detail of construction isn't viewed so your input is helpful.
-
01-30-2020, 07:46 AM #10
-
03-11-2020, 08:17 AM #11
Re: Foundation consists of two different sized block walls.
Jerry, thanks for the input.
Here's photo of what should be done.
Also, tap the mortared area with a screw driver: hollow sound=not done right, solid thump sound="appears" to be correct.right angle mortar2.JPG