    Default This is not right...

    So, who's wrong? This is from a 50 year old home with some kitchen upgrades including repiping of the hot water line. The disposal had been removed and not replaced.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Oct 2014
    Location
    Maryland, DC, and Northern Virginia, electrical only
    Posts
    460

    Default Re: This is not right...

    Where's the trap?


  3. #3
    Join Date
    Jun 2012
    Location
    Escondido, CA
    Posts
    34

    Default Re: This is not right...

    The trap is made of black plastic pipe, connected to the white plastic. The issue is the copper water line installed over the under-sink receptacle. Why would a plumber intentionally do that? Of coarse, why would the electrician install the receptacle within a couple inches of the cabinet base? Two wrongs don't make it right.


  4. #4
    Join Date
    Oct 2014
    Location
    Maryland, DC, and Northern Virginia, electrical only
    Posts
    460

    Default Re: This is not right...

    I'll certainly take your word that it's a copper water line in front of the receptacle, rather than something flexible and easily shiftable. Doctrine on receptacles under sources of moisture has changed regularly over the past few Code cycles, but until recently having a receptacle there without a "GFCI/AFCI-protected" sticker and maybe a TR marking on it was legal--still is, in most jurisdictions. Access blocked? 110.12, maybe: not workmanlike. The parent language of 110.26, but probably not the clauses, as receptacles are generally not treating as requiring examination etc. Unless you can show that the water line is likely to leak. Now if rather than being grandfathered, or protected by an electronic CB, you tried to replace it with with a GFCI receptacle, IMO it would violate the "readily accessible" requirement as presently blocked: 406.4(D).

    I agree, BTW, that two wrongs usually don't make a right; furthermore, three rights don't always make a left.


  5. #5
    Join Date
    Mar 2007
    Location
    Knoxville, TN
    Posts
    2,560

    Default Re: This is not right...

    Is the outlet active?

    - - - Updated - - -

    Is the outlet active?


  6. #6
    Join Date
    Jun 2012
    Location
    Escondido, CA
    Posts
    34

    Default Re: This is not right...

    Yes, Jack, the receptacle was active/energized.