    this is a gas line in the attic. Any problems with this lying over a light fixture?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: gas line / fixture

    I would definitely write that up. The gas line should be re-routed away from the light fixture and be properly secured according to the manufacturer's specs. In fact, I don't believe it should be lying on top of the ceiling without protection. Someone could run a screw up from the bottom and pierce the CSST.


  3. #3
    Nolan Kienitz's Avatar
    Nolan Kienitz Guest

    Default Re: gas line / fixture

    Jerome,

    Here is a URL for the Gastite installation guide. Section 4.0 has the installation guidelines.

    http://www.gastite.com/include/langu...IGuide2008.pdf


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: gas line / fixture

    Jerome,

    As John and Nolan pointed out:

    4.1 d)
    Protect tubing from contact with sharp objects

    (I.e., the corners of that recessed light fixture.)

    4.1 3)
    Avoid stressing the tubing ...

    (I.e., pulling on that fitting as shown in your photo.)

    4.4 Strike Protection

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Jerome W. Young's Avatar
    Jerome W. Young Guest

    Default Re: gas line / fixture

    Roger thanks