I have no questions, I just wanted to share a recent inspection experience for entertainment purposes. I was inspecting an electrical raceway and breaker box beneath a deck when I went to open the box door, sparks flew and I saw my life flash before my eyes. I did some investigating and discovered improper wiring at the hot tub. I detected voltage at the hot tub body, breaker box, raceway running the length of the house, the A/C cabinet and disconnect box. I have never run across this serious of a hazard on the exterior of a home before. It may be unrelated but the family dog "spike" was buried in the backyard.
Dave in Kansas
Similar Threads:
-
03-10-2008, 09:31 PM #2
Re: Electrifying Inspection
Lucky you. Sounds like it could have been much worse.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
03-11-2008, 05:58 AM #3
Re: Electrifying Inspection
Hi,
I not saying you don't have a problem here, but I hope you are not just relying on that voltage ticker. They are able to pick up voltage inside the conduit and it does not necessarily mean the conduit is energized.
-
03-11-2008, 06:05 AM #4
Re: Electrifying Inspection
I agree. Those suckers are tricky. I have discovered "hot" unprotected wires that on further investigation turned out to be disconnected on both ends. The voltage sniffer was picking up induced current because the disconnected wire was running alongside energized wires. The sniffer I use has adjustable sensitivity, which helps some.
-
03-11-2008, 06:08 AM #5
Re: Electrifying Inspection
David
Was the hot tub protected by an GFCI? Doesn't sound like it is given your findings I would have expected it to trip.
-