    Default Bundled conductors

    I am looking for some info. on how conductors are allowed to be bundled inside panleboards. Any help would be appreciated. Take a look a these pictures. This panel dates back to 1975.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral
    Greg Jenkins

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Bundled conductors

    Typically, in a panelboard that is not a problem because you have less than 24" conductors that way, however, ...


    ... in your photos, you will see that the conductors go down, are bent into a 'U' and go back up, so they may well be greater than 24" bundled up. The easy solution is to bend the conductors to the breakers as they come down to where the breakers are, cutting off the excess length - problem solved.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Charleston, WV
    Posts
    77

    Default Re: Bundled conductors

    Is there any reference to this in the nec?

    Greg Jenkins

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Bundled conductors

    Quote Originally Posted by Greg Jenkins View Post
    Is there any reference to this in the nec?
    To bundling? Yes.

    If you mean "within a panel enclosure", yes, that is included in the *general statement* about bundling and lack of maintaining space.

    Doubling those conductors back over themselves as shown simply doubles the number of conductors to be counted. The intent is to allow heat to ventilate out from the conductor, more conductors traps more heat in, bending them back over themselves does the same thing - there are still that many carrying current and the associated heat.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Charleston, WV
    Posts
    77

    Default Re: Bundled conductors

    Thanks Jerry!

    Greg Jenkins

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •