Who needs 6" of clearance for single wall
Found this today.........
Similar Threads:
-
04-27-2007, 03:59 PM #2
Re: Who needs 6" of clearance for single wall
Single wall? In an attic? There's more than a clearance issue.
Eric Barker, ACI
Lake Barrington, IL
-
04-27-2007, 04:28 PM #3
Re: Who needs 6" of clearance for single wall
Flue should be double-wall constructed where it passes through a ceiling or roof decking and have a (1) inch clearance from combustible material.
6" clearance? Not sure what your meaning.
-
04-27-2007, 06:04 PM #4
Re: Who needs 6" of clearance for single wall
Good catch....you saved a life or two that day!
-
04-27-2007, 10:13 PM #5
Re: Who needs 6" of clearance for single wall
Maybe I wasnt aware that single wall vent was not allowed in attic, my bad. But as far as the 6" rule as far as I know single wall vent has to be 6" from any combustibles. If anyone can educate me further I welcome it.
-
04-28-2007, 06:17 PM #6
Re: Who needs 6" of clearance for single wall
Vent connector clearances:
gas single walled- 6"
B-vent- 1"
Oil single walled-18" unless listing states 9"
L-vent- 6-9" per listing except for pellet venting
pellet L vent-1-3" depending upon listing
wood single walled-18"
wood double walled close clearance -6"
No single walled connectors outside the thermal envelope such as attics or crawl spaces. Too much condensation and weaker draft.