Results 1 to 20 of 20
    Ryan Stouffer's Avatar
    Ryan Stouffer Guest
    Default Neutrals and grounds
    Nice panel
    Ryan Stouffer Guest
    Default Re: Neutrals and grounds
    New post
    Apr 2009
    NY State
    They occupy the same bar in the service equipment or main panel.
    No offense meant, but shouldn't common topics like this be covered in the training courses? Isn't there any requirement to shadow an experienced inspector before doing this on your own?
    I commend you for asking questions as that is how we all learn. But how good can the inspection be when the common topics still need to be covered?
    Couple of black conductors there need to be properly marked as grounded/neutral conductors.
    Apr 2009
    NY State
    I see one grounded conductor and it is white.
    I don't see a grounded conductor for that 100A breaker on the left.
    There is no requirement that a grounding electrode conductor or bonding conductor be green.
    Quote Originally Posted by Ryan Stouffer View Post
    Nice panel
    I am not sure why you posted this. Are you looking for feedback on something in particular?
    Gunnar - For some reason he deleted his question about whether neutrals and grounds needed to be on the same bar in the service equipment.
    Apr 2009
    NY State
    Wow. I just noticed that.
    WHY do original posters do that???? Makes the whole thread useless.
    John,
    Thanks. I thought I was being EXTRA dense today. Good to know that I am just regular dense.
    Apr 2009
    Manchester, Vermont
    If the wires are feed in thru conduit, I believe you would have to duct seal
    around all the wires to seal the conduit openning.
    Apr 2009
    NY State
    Quote Originally Posted by Robert S. Mattison View Post
    around all the wires to seal the conduit conduit openning.
    I have never heard of such a requirement.
    Peter,
    I believe he is referring to sealing required for raceways which go down into the ground.
    Apr 2009
    Manchester, Vermont
    My reply in my last post comes from, the NEC 2008 edition:
    300.5(G) Raceway Seals
    300.7 Raceway Exposed to Different Temperatures
    Borrowing the thread for a moment, for today's jewel of a neutral.... I now return you to your regularly scheduled programming....
    BTW, what section of the NEC governs the splicing of SECs?
    - 230.46 Spliced Conductors.
    - - Service-entrance conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15.
    Vancouver - Canada
    Jerry, Since I'm a little north of you, I'm not familiar with the NEC but doesn't that sentance refer to splicing of the actual feeder cable (ie: extending it) and not splicing the branch circuit wires to the feeder (as in lack of neutral bar) ?
    Also, does the NEC allow all the branch circuit wiring to enter and pass through the main-switch compartment ?
    Just curious.
    Joe Klampfer RHI
    www.myinspection.ca
    Pacific Home Inspections
    Quote Originally Posted by Joe Klampfer View Post
    Joe,
    The question was about "service entrance conductors", thus the reference to splices for service entrance conductors, not feeders or branch circuits.
    No. I believe you are referring to using the panel as a "raceway", i.e., "does the NEC allow all the branch circuit wiring to enter and pass through", and all the conductors in the panel are to be terminated in that panel, either at the grounding terminals, neutral terminals, or at an overcurrent device. This means that "passing through" is not allowed.
    Vancouver - Canada
    Sorry Jerry, I thought we were both talking about the photos in post # 15 above.
    Joe Klampfer RHI
    www.myinspection.ca