Results 1 to 17 of 17
Thread: Handrails on deck
10-04-2009, 09:22 AM #1
Handrails on deck
disregard this post
Similar Threads:Last edited by Ryan Stouffer; 10-04-2009 at 09:35 AM.
10-04-2009, 09:38 AM #2
Re: Handrails on deck
Just clarifying, yes, that needs handrails.
10-04-2009, 09:41 AM #3
Jerry, it does need handrails because it is considered 4 or more risers. Correct?
10-04-2009, 09:43 AM #4
Ryan,
Correct.
10-04-2009, 09:54 AM #5
Thanks. With rookies like myself, I just want to make sure.
10-04-2009, 02:08 PM #6
disregarded!
10-04-2009, 09:50 PM #7
LOL it's only 3 1/2 risers, which brings another code issue into play.
10-05-2009, 09:14 AM #8
What is the code for steps? I thought you could have 1 step without a hand rail, after that you needed something.
10-05-2009, 11:52 AM #9
4 or more risers.
10-05-2009, 12:15 PM #10
whose the moderator
10-05-2009, 02:57 PM #11
Any change in elevation is a "riser", which must conform to the dimensional tolerances of the code and the maximum variation from the other risers.
I'm not sure what the UBC says.
No minimum in the IRC, 4" minimum in the IBC; 7-3/4" maximum in the IRC and 7" maximum in the IBC.Usually the min-max riser can be at least 6" to 9.5 max.
The tolerance is 3/8" between adjacent risers and 3/8" between the highest and the shortest risers.The tolerance for multiple risers are + or - 1/4" at the most.
The 4 or more rises come into play because the code say 4 or more risers and does not address a height.A hand rail is not required if the top landing is not over 24" from grade. So that is where the 4 riser comes into play.
If the stairway, deck, etc., is more than 30" high above the level below, then a guard rail is required. Maybe that is what you were thinking of?
10-05-2009, 09:30 PM #12
In my State (Mass.) 3+ risers require handrails regardless of related heights.
(e.g. 30" for decks, landings,etc)
10-08-2009, 06:09 PM #13
10-09-2009, 12:29 PM #14
Ben,
There still is no conflict.
That does not mean one does not, should not, use common sense for each of the two distinct and different things.
If you have 4 risers of 7" high then the total height is 28" - which means no guard on the stairs and no guard on the deck, but it does required a handrail on the stairs.
If you have 4 risers of 7-3/4" then the total height is 31" - which means a guard is now required on the stairs and on the deck, along with the handrail on the stairs.
However, each (the guard and the handrail) serves a different purpose.
10-09-2009, 01:52 PM #15
01-29-2010, 01:55 PM #16
Not only that stair needs a handrail but the BC code suggest If width is more than 1100mm a handrail is required to have both sides of the stairs.
01-29-2010, 08:00 PM #17