Results 1 to 4 of 4

Thread: Ground wire

  1. #1
    Ryan Stouffer's Avatar
    Ryan Stouffer Guest

    Default Ground wire

    Does the service entrance ground wire have to be sheathed?

    Thanks,

    Ryan

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Apr 2009
    Location
    NY State
    Posts
    443

    Default Re: Ground wire

    No, but #6 or #8 ground wires should be free from physical damage once they leave the enclosure.
    Looks like they sleeved that in PVC. Even though Sch40 does not offer any physical protection it is better than nothing at all. Depends on the location.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Ground wire

    No.

    But ... the ground should go to the ground terminal shown on the right in that photo.

    Also, the neutral conductor insulation behind the ground conductor looks melted/overheated. Could be anti-oxidant paste, but looks overheated.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Apr 2009
    Location
    Manchester, Vermont
    Posts
    298

    Default Re: Ground wire

    Rayan Stouffer

    Quote: "Does the Service entrance ground wire have to be sheathed?"

    SE-R cable is used above ground, it carries three insulated wires and one non-
    insulated wire. It your case this is the ground wire.

    So the ground wire doesn't have to be sheated or jacketed in insulated,
    only the ground wire used in URD cabe is insulated.

    Aluminum wire in direct contact with the earth shall be provideed with
    corrosion protection. So SE-U or SE-R should not be burried.