Results 1 to 37 of 37
Thread: Fuse panel
10-17-2009, 09:01 PM #1
Fuse panel
This 1914 house has a 100 A fused disconnect and a large fuse panel. Around here, 60 Amp is more typical for places of this age. Could this be a 1940's upgrade?
The neutral bus appears to be isolated in the distribution panel. If the buyer replaces all the incorrect fuses, does he have a safe installation?
I know the selection of fuse ratings is a disaster. This place has been a rental for years and tenants have probably blown a lot of fuses with their plug-in space heaters, hence the over-fused circuits everywhere.
10-17-2009, 09:40 PM #2
Re: Fuse panel
Looks like that panel has been on fire in the past ?
10-18-2009, 12:29 AM #3
Re: Fuse panel
Looks like a newer fuse panel to me, but don't see many any more.
Any time I see improper fuses in place, which is almost always, I recommend replacement of the fuses with type S fuses.
10-18-2009, 06:51 AM #4
Re: Fuse panel
Then NEC *REQUIRES* that those Edison base type fuses be replaced with the safety type fuses and the insertion of the safety type fuse adapters whenever overfusing is found - no, they are not allowed to go back to the correct size Edison base fuse but must install the correct size adapter and the correct size safety fuse, or, change to another type of fuse (cartridge fuse) or breaker - meaning there are options, but the safety type fuse adapters are the least expensive option I can think of.
From the 2008 NEC:
- 240.51 Edison-Base Fuses.
- - (B) Replacement Only. Plug fuses of the Edison-base type shall be used only for replacements in existing installations where there is no evidence of overfusing or tampering.
I see the smoke residue Ron is referring to right across the top of the fuse panel.
John,
"The neutral bus appears to be isolated in the distribution panel." - It does look that way in the photo, but you had a better look.
"If the buyer replaces all the incorrect fuses, does he have a safe installation?" - *I* would not use the term "safe installation" ... even if the fuses were all replaced with safety fuse adapters and safety fuses ... even safety fuses can be wrapped in aluminum foil (I've seen it) and inserted, defeating the safety feature of the fuse, but they are a lot better than the Edison base fuses in that they are more resistant to tampering by making it harder to tamper with them.
10-18-2009, 09:44 AM #5
Re: Fuse panel
Any idiot can modify a breaker panel as well. All it takes is someone smart enough to pull the panel cover off. Adding a larger breaker is about as easy as stacking Legos. Or, they could just directly solder the wire in lieu of purchasing a breaker.even if the fuses were all replaced with safety fuse adapters and safety fuses ... even safety fuses can be wrapped in aluminum foil (I've seen it) and inserted, defeating the safety feature of the fuse, but they are a lot better than the Edison base fuses in that they are more resistant to tampering by making it harder to tamper with them.
10-18-2009, 12:38 PM #6
Re: Fuse panel
"All it takes is someone smart enough to pull the panel cover off."
The thing with fuse panels, though
, is that ...
*you do not even need to pull the cover off* ...
All you have to do is unscrew that little bugger and screw in a higher amperage fuse (if using the old Edison base fuses).
And, when that 30 amp fuse blows, simply put a penny behind the fuse, no more problemo.
10-18-2009, 01:30 PM #7
Re: Fuse panel
Along the line of what Jerry is saying, I went to the hardware store to get a fuse, they only sold 30amp.
Their thinking is why stock 4or 5 different fuses when 1 size fits all.
10-18-2009, 03:24 PM #8
Re: Fuse panel
10-18-2009, 03:52 PM #9
Re: Fuse panel
Yes, I suspect some #14 wire has been fried in this panel in the past.
The little breaker fuse adaptors are cool, but these are all rated for 20 A.
Agreed, the hazard of tampering is always there. The landlord owner has been ignorant not to check the fuse ratings, and lucky for him and his tenants this place hasn't had a serious fire yet.JP *I* would not use the term "safe installation" ... even if the fuses were all replaced with safety fuse adapters and safety fuses ... even safety fuses can be wrapped in aluminum foil (I've seen it) and inserted, defeating the safety feature of the fuse, but they are a lot better than the Edison base fuses in that they are more resistant to tampering by making it harder to tamper with them.
My client realizes he should install a breaker panel, plus I told him he should, but there's a roof to put on and windows to replace, etc. He plans to put in the correct 15 Amp fuses. Hopefully, Type S are all that's available.
10-18-2009, 04:12 PM #10
Re: Fuse panel
10-18-2009, 07:33 PM #11
Re: Fuse panel
Most of the branch circuits are #14 copper, should have 15 A fuses, as marked on the panel, pic 1. People have installed larger fuses, so we are speculating a fire may have been caused in the past by over-fusing??
Those mini-breakers in the panel are wrong, as they are rated for 20 A.
10-18-2009, 07:48 PM #12
Re: Fuse panel
Which, IF the Canadian Electrical Code is as the NEC is, the proper sized Edison base fuses ARE NOT allowed to be re-installed in that fuse panel - only the safety fuse adapters with safety fuses would be, or replace the fuse panel with a modern breaker panelboard.
Do you know if the Canadian Electrical Code has the same type limitation for replacement of Edison base fuses?
10-18-2009, 09:30 PM #13
Re: Fuse panel
I dont have my code book but I am quite sure all fuses are required by the canadian electrical code to be replaced with the safety type fuses. I will double check when I get home.
10-19-2009, 12:12 AM #14
10-19-2009, 04:02 AM #15
10-19-2009, 06:00 AM #16
10-19-2009, 06:02 AM #17
Re: Fuse panel
As an insurance inspector..I can tell you that my instructions by the insurance company when ever I come across a plug fuse panel..is the classify it as a risk..As a home inspector, I always recommend replacement of plug fuse panels..more so if the buyer plans on renting..
10-19-2009, 06:07 AM #18
Re: Fuse panel
Why not just spend the $300 or $400 and replace the entire panel with 15amp breakers.
The insurance company would be happier and might reduce the premium. (After a 4point inspection)
10-19-2009, 06:34 AM #19
Re: Fuse panel
First off, that panel looks more like a late 50's or early 60's vintage, and not from 1914 at all. At first glance, the wires liikmlike they might be large enough for a 100 amp service, so no problem there.
I note that many of the fuses have been replaced by circuit breakers. This being the case, there is no need to use 'type S' fuses. The breakers are fine. I have a direct ruling on this from the code panel. Replacing the fuses with breakers removes the need for using tamper-resistant fuses.
10-19-2009, 08:24 AM #20
Re: Fuse panel
10-19-2009, 08:33 AM #21
Re: Fuse panel
Ken,
I will cost a lot more than that to replace that panel, probably more like $1,000 to $1,500.
You are not allowed to just remove the fuse panel inside that enclosure and install a breaker panelboard in that same enclosure, you need to replace the enclosure too.
John,
Do you have that ruling you could post? Thank you.
I doubt it allows replacing 15 amp Edison base plug fuses with 20 amp Edison base plug breakers, and nothing in the NEC says you are allowed to do that instead of installing the safety fuse adapters.
I would be very interested in seeing their ruling and its wording.
10-19-2009, 02:24 PM #22
Re: Fuse panel
There appears to be evidence of branch circuit overheating in the panel. My best guess would be a late 1950's upgrade, which is now a fire waiting to happen. There appear to be signs of overheated neutrals and overheated hot conductors. The best recommendation, in my opinion, would be referral to an electrician and recommendation to replace. I would love to be there when the panel was de-energized, unmounted, and the bus bars inspected. My guess is they will show signs of overheating. That, then, begs the question: what about the branch circuits? Unsafe, in my opinion.
Randall Aldering GHI BAOM MSM
Housesmithe Inspection
www.housesmithe.com
10-19-2009, 06:08 PM #23
10-19-2009, 06:12 PM #24
10-19-2009, 06:43 PM #25
Re: Fuse panel
I don't give buyers any other advise but remove and replace if its had any kind of smoke or past fire condiiton. and any of these old fuse panels need to go.A.S.A.P.
bEST
rON
10-19-2009, 08:25 PM #26
10-20-2009, 12:45 AM #27
Re: Fuse panel
CEC 14-204
(1) Where plug fuses are used in branch circuits, they shall be of such a type and installed so tat they are non-interchageable with a fuse of larger rating.
I hope that helps
10-20-2009, 02:36 AM #28
Re: Fuse panel
Nothing wrong with the fused disconnect if it's service rated. However, for the extra a main breaker in a panel costs I'd certainly replace it as part of installing a new panel.
Most heat damaged branch circuit wiring I see is caused by loose connections and seldom by oversized fuses or breakers.
10-20-2009, 07:25 AM #29
Re: Fuse panel
10-20-2009, 07:27 AM #30
Re: Fuse panel
10-20-2009, 10:06 PM #31
10-21-2009, 06:02 AM #32
Re: Fuse panel
Yes, the utility would have to cut power by pulling the meter. And depending on locality you would need to pull a permit. Once power is off you can install the new panel, run any new lines, as needed to the meter and have a brand new service. If the original disconnect is okay, you could avoid the meter pull by using the disconnect and leaving it in place.
I would never advise anyone to do this hot. (Flash Arc with ~3,000 amps isn't nice)
10-21-2009, 06:28 AM #33
Re: Fuse panel
Now you tell me! No worries though, the sensation has returned to my right side, my fingerprints are coming back in, and my eyesight grows less fuzzy by the day.
Actually, I did hot wire a 96kVA step-down transformer once, when I was young, and definitely very stupid. Knowing what I know now, I'm not sure how I escaped winning a Darwin Award.
10-23-2009, 06:24 AM #34
Re: Fuse panel
"Panel Statement: 240.51 is dealing solely with Edison base fuses. There is
nothing in the Code to prohibit the use of the circuit breakers that the submitter
references where used as replacements only."
That is the response by the code committee to a proposal I made, seeking to clarify this matter in the 2008 edition of the NEC.
This response is included in the 'report on proposals 2008.' Look at page 70-169, proposal 10-46 Log #1654 NEC P-10.
In effect, they told me "This is about FUSES, not circuit breakers - what part of that do you fail to understand?" The code is absolutely silent about edison-base circuit breakers.
10-23-2009, 04:39 PM #35
Re: Fuse panel
Which in no way addresses the "overfusing" aspect.
All that is saying is that, yes, if you have Edison base fuses OF THE PROPER RATING and want to replace those Edison base fuses with Edison base circuit breakers OF THE SAME PROPER RATING, there is no prohibition against that.
You trying to turn that around and say it allows you to take overfused Edison base fuses out and install proper size Edison base circuit breakers is adding something completely new to the equation.
The code DOES address EXACTLY WHAT TO DO when Edison base fuses have been "overfused" - the code REQUIRES the installation of safety type fuses and their adapters. Then the question becomes, do they make those safety type base circuit breakers in the appropriate sizes for the safety type bases?
10-26-2009, 04:38 AM #36
Re: Fuse panel
Sorry, Jerry, but the panel didn't see it that way when I made my proposal. As far as they're concerned, breakers and fuses are as different as cheese and chalk. It would seem that the panel did not see a reason to fear 'over breakering.' I made my proposal specifically because of the reasoning you put forth - and the panel saw no need. As they say, code already allows you to replace a fuse with a breaker - even if that fuse was too big.
And. naturally, there is absolutely no prohibition of replacing fuses with breakers - or nearly every service change made would be a 'violation.'
Perhaps the panel was reassured by the fact that you can reset breakers - no more 10PM Sunday night scrambles to find more fuses!
To be fair, this debate has benn going in circles since the 70's. The same tired rhetoric, again and again. I doubt the panel is going to ever re-write the code to specifically address every way someone can misunderstand things; it would seem plain that if there's no longer any fuse, over-fusing cannot be an issue.
10-26-2009, 06:29 AM #37
Re: Fuse panel
Sorry John, but YOU are reading WAY TOO MUCH into what you posted they said.
THEY DID NOT SAY what you are saying they said - not if you post their accurate answer (and I have no reason to suspect you did anything else, I am only relying on the information *you* provided).
