    Does the IRC state that a secondary drain line has to terminate at a conspicuous location and if so where do I find it?
    Default Re: A/C secondary drain line
    From the 2006 IRC
    M1411.3.1 Auxiliary and secondary drain systems.
    In
    addition to the requirements of Section M1411.3, a secondary
    drain or auxiliary drain pan shall be required for each
    cooling or evaporator coil where damage to any building
    components will occur as a result of overflow from the
    equipment drain pan or stoppage in the condensate drain
    piping. Such piping shall maintain a minimum horizontal
    slope in the direction of discharge of not less than
    1/8 unit
    vertical in 12 units horizontal (1-percent slope). Drain piping
    shall be a minimum of
    3/4-inch (19 mm) nominal pipe
    size. One of the following methods shall be used:
    1. An auxiliary drain pan with a separate drain shall be
    installed under the coils on which condensation will
    occur. The auxiliary pan drain shall discharge to a
    conspicuous point of disposal to alert occupants in the
    event of a stoppage of the primary drain. The pan shall
    have a minimum depth of 1.5 inches (38 mm), shall
    not be less than 3 inches (76 mm) larger than the unit
    or the coil dimensions in width and length and shall be
    constructed of corrosion-resistant material. Metallic
    pans shall have a minimum thickness of not less than
    0.0276-inch (0.7 mm) galvanized sheet metal. Nonmetallic
    less than 0.0625 inch (1.6 mm).
    2. A separate overflow drain line shall be connected to
    the drain pan provided with the equipment. This overflow
    drain shall discharge to a conspicuous point of
    disposal to alert occupants in the event of a stoppage
    of the primary drain. The overflow drain line shall
    connect to the drain pan at a higher level than the primary
    drain connection.
    3. An auxiliary drain pan without a separate drain line
    shall be installed under the coils on which condensate
    will occur. This pan shall be equipped with a water
    level detection device conforming to UL 508 that will
    shut off the equipment served prior to overflow of the
    pan. The auxiliary drain pan shall be constructed in
    accordance with Item 1 of this section.
    4. A water level detection device conforming to UL 508
    shall be provided that will shut off the equipment
    served in the event that the primary drain is blocked.
    The device shall be installed in the primary drain line,
    the overflow drain line or the equipment-supplied
    drain pan, located at a point higher than the primary
    drain line connection and below the overflow rim of
    such pan."
    Aug 2009
    rockport texas
    Default Re:Tankless water heaters
    It's time to replace my water heater. I've read some responses about tankless water heaters. Does anyone have any experience with external mounted tankless water heaters? I live in South Texas so weather isn't a concern.
    Stanley,
    If your looking to install a tankless gas water heater, your probably looking at having to update your gas service line to a larger size.
    If not, a gas tankless is not going to work efficiently.
    Richard Stanley's Avatar
    Richard Stanley Guest
    I would not install it outside in your corrosive environment. It will rust before you put away the tools.
    My next one will be tankless (electric).
    imported_John Smith's Avatar
    imported_John Smith Guest
    Im interested why you want the tankless water heaters. In Houston, our cold water generally runs ~78F (except for our month of winter). I dont see the cost of heating water in the tank being that great as compared to the cost of the tankless systems. Just wondering what your motivation was.
    I have always wondered why a trap is required in the primary condensate drain from the A/C. The secondary drain does not have one. Is this only necessary when the primary drain is connected to the household sewer piping, or is it always required. And, if required, why not the secondary drain? When the furnace or air conditioner is operating, the coil box is under positive pressure and heated or cooled air will escape out of the secondary drain pipe.
    Because that drawing from that manufacturer is one of the only ones not to specify that the secondary condensate line be trapped too - to keep the units from sucking air in or blowing air out through the condensate lines.
    Now, as to what THAT manufacturer does not show the secondary being trapped ... that is beyond me. I would call them and ask them to explain that to me, and if the secondary drain does need to be trapped (as one would think it would) would they kindly send me a revised drawing showing it. I've done that with various appliances and manufacturers over the years and you would be surprised how often the engineering department goes ... 'Ummm ... I don't know why that is drawn/stated like that, it certainly should not be.', followed by some more discussion and 'I will fax/email the revised installation instructions to you as soon as we have them revised, you might get them later today or tomorrow, we will start working on it right away.', and they do.
    Thanks JP. Apparently, I will now have to update my diagram for my reports. Does anyone have a correct diagram with the proper traps?
    I did a home this weekend that was a new install. HVAC contractor was miffed because I called it out in my report. Copied the info off the evaporator coil and pulled up the install instructions off the internet. Cant hardly argue when the manufacturer calls for it.
    See page 4 of the attachment.
    From that page 4: note the plural aspect of the requirement (bold is mine)
    9. Make sure that outlet of each trap is below its connection to condensate pan to prevent condensate from overflowing drain pan. Prime all traps, test for leaks, and insulate traps and lines if located above a living area. Consult local codes for additional restrictions or precautions.
    Note, however, that the drawing on page 4 shows a "running trap", which is not allowed. Sometimes all you can do is wonder about the engineers and technical writers who write and draw those installation instructions.
    From a Rheem/Rudd installation instructions - see attached.
    I agree Jerry, but, I recall several references in IRC stating "or manufacturers instructions", probably not verbatim, but along the same lines.
    Close ... but no cigar. (see bold red text below)
    - CHAPTER 14
    - - HEATING AND COOLING EQUIPMENT
    - - - SECTION M1401
    - - - - GENERAL
    - - - - - M1401.1 Installation. Heating and cooling equipment and appliances shall be installed in accordance with the manufacturer’s installation instructions and the requirements of this code.
    Of course, though, the code then says:
    - M1411.3 Condensate disposal. Condensate from all cooling coils or evaporators shall be conveyed from the drain pan outlet to an approved place of disposal. Condensate shall not discharge into a street, alley or other areas where it would cause a nuisance.
    - - M1411.3.1 Auxiliary and secondary drain systems. In addition to the requirements of Section M1411.3, a secondary drain or auxiliary drain pan shall be required for each cooling or evaporator coil where damage to any building components will occur as a result of overflow from the equipment drain pan or stoppage in the condensate drain piping. Such piping shall maintain a minimum horizontal slope in the direction of discharge of not less than 1/8 unit vertical in 12 units horizontal (1-percent slope). Drain piping shall be a minimum of 3/4-inch (19 mm) nominal pipe size. One of the following methods shall be used:
    - - - (then lists 4 methods)
    Thus, when specified by the manufacturer, *it shall be done*, and when specified by the code, *it shall be done*... i.e., when specified by either one, *it shall be done*.
    In the drawing Gunnar posted, it was not shown in the manufacturer's drawing, but - was it stated in the text of the installation instructions? If so, it was required, if no, that particular manufacturer did not require it, but ... if you call them and question them on it, I am sure it was an unintentional slight and that they will fix it.
    Here is an example of an intentional slight I ran across in the Virginia Uniform Building Code today:
    There is a section requiring door viewers in door entrance doors, unless there is view panels in the door, and the code stated that the *minimum*, yes, the *minimum* angle of viewing is ... drum roll ... 180 degrees.
    Now, I don't know about any one else, but "180 degrees" is just what it says, and *I* cannot look out a glass door and see "180 degrees", much less any type of viewer I have ever seen. Try this - stand at your window and look out, can you see "180 degrees"?
    The only way to see "180 degrees" is to bump the window out so it projects out past the wall the window is mounted in. Try that with a door view panel, much less a door viewer - even those wide angle viewers.
    Technically, the super duper pooper scooper 200 degree wide angle door viewers are rated at that, but put them in a door and the jambs block the view to each side, unless, again, the door is projecting out from the adjacent wall.
    Darrel Hood's Avatar
    Darrel Hood Guest
    I am beginning to frequently see moisture sensors installed in the primary condensate drain so they turn off the equipment if they sense moisture elevation. No secondary drain line is installed. I don't trust them and have not been able to find anything that allows this configuration. Am I missing something as usual?
    Darrel Hood
    DILIGENT PROPERTY SERVICES
    Aug 2009
    rockport texas
    darrel
    IRC 2006 check M1411.3.1 Auxiliary and secondary drain systems, #3and #4
    Hmmm, so I guess I should include the 3/4" pvc condensate drain from the AC cemented into the basement cement floor from yesterday in my report. picky picky
    House also had a great ventilation feature. I could stand in the basement and see the outside through the running foundation wall crack. I guess that eliminates the need for an xfan in the basement bath.
    This report is going to be sooo long. Taking a quick break from it right now.
    RobertSmith's Avatar
    RobertSmith Guest
    Are secondary lines required to be insulated, either by code or manufacturer?
    Quote Originally Posted by RobertSmith View Post
    The secondary isn't mentioned in Florida Code:
    FBC 307.2.5 Pipe insulation. All horizontal primary condensate drains within unconditioned areas shall be insulated to prevent condensation from forming on the exterior of the drain pipe.
    However, I've read AHU install guides that state "Insulate the drain lines where sweating can cause water damage." They don't differentiate between primary and secondary in the text.
    I don't know about the IRC.
    Dom.
    Jan 2010
    Dom.
    Around here they only trap condensate with the draw through units and not the blow through.. running traps are only used with heat pumps.. soooooooooo??? I have never questioned, should I? what is the consequence? Thanks!
    Quote Originally Posted by kenny martin View Post
    Kenny,
    Running traps are not allowed (unless a running trap is specifically referenced as being allowed/required in the installation instructions).
    Some of the 'blow through' units do specifically state that a condensate trap is not required ... then the installation instructions hedge for wiggle room by adding: 'however, not installing a condensate trap will lead to a loss of efficiency" ... so why spend the extra money to buy a high efficiency unit and then blow all that savings out the condensate drain piping?
    Those don't need a trap, except that they do to maintain their efficiency rating ... ? Huh? Does not make much, if any, sense, does it?
    Jan 2010
    Kenny,
    ?? I hate code writers!! And some manufacturers especially when things aren't written to be fully understood unless you are already an experienced pro! Makes me head hurt!!!