Ungrounded exterior receptacle outlet on a circuit protected by a GFCI breaker OK?
Is an existing ungrounded exterior receptacle outlet mounted in a compliant outlet box allowed if it is protected by a GFCI breaker?
- Thanks
Similar Threads:
-
10-18-2009, 04:14 PM #2
Re: Ungrounded exterior receptacle outlet on a circuit protected by a GFCI breaker OK
Yes.
And required to be if that receptacle has been replaced.
-
10-18-2009, 05:00 PM #3
Re: Ungrounded exterior receptacle outlet on a circuit protected by a GFCI breaker OK
Thanks.
-
10-27-2009, 12:06 PM #4
-
10-27-2009, 09:04 PM #5
Re: Ungrounded exterior receptacle outlet on a circuit protected by a GFCI breaker OK
Is 'no equipment ground' labeling required as it would be indoors? I'm thinking yes and am almost feeling dumb for asking.
-
10-28-2009, 04:01 AM #6
Re: Ungrounded exterior receptacle outlet on a circuit protected by a GFCI breaker OK
"Is 'no equipment ground' labeling required as it would be indoors? "
Yes
' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.