    Hello everyone. I am new and in dire need of some help. I am very confused. I had my basement inspected and it failed because i needed to have a firestop above my fireplace. I just had the HVAC company that installed it come out and make it code compliant, but all they did was put some sheet metal around the flue. The city inspector said i need to put some insulation around it or something, but i have read alot about how it is NOT compliant to put insulation around the flue. Is this right? What else needs to be done? Do i need to put some plywood at the bottom of the floor joice under the flue?

    Thank you all very much for your help.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: Fire stop for gas FP in basement

    ask the person who is inspecting to come back and reinspect.
    stop thinking


  3. #3
    Tyler Kent's Avatar
    Tyler Kent Guest

    Default Re: Fire stop for gas FP in basement

    thank you. i will stop worrying about it. I have him scheduled to come out Monday morning and just wanted to make sure it was good before he comes out and it ends up costing me more money to have it inspected a 3rd time.


  4. #4
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: Fire stop for gas FP in basement

    if they are charging you I would call first and get exactly /do what that guy wants.


  5. #5
    Richard Pultar's Avatar
    Richard Pultar Guest

    Default Re: Fire stop for gas FP in basement

    it looks like that metal might have gone where the vent penitrated the wall


  6. #6
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: Fire stop for gas FP in basement

    Can you provide the make and model fireplace?

    There should be a listed firestop at the ceiling level installed per the listing. If the listing does not allow for caulking then you cannot do it without voiding the warranty and listing. You certainly can NOT install insulation against the pipe or encroach on the stated clearances. In fact, anywhere insulation could come in contact, you are required to install an insulation shield. The space around the metal firestop is called 'fireblocking' and must comply with the IRC 602.8 or whatever equivalent your code has. This entire chase appears to be open. BTW, firestops must be listed and cannot be site fabricated from blank sheetmetal.

    I highly recommend you get a hearth pro in there to make these corrections and ensure proper installation. The mfr. of the fireplace should be able to provide a list of dealers near you. You can also go to NFI Certified to locate the NFI Certified Specialist nearest you.

    Bob

    Keep the fire in the fireplace.

  7. #7
    Tyler Kent's Avatar
    Tyler Kent Guest

    Default Re: Fire stop for gas FP in basement

    The fireplace is a Continental CDV33 REAR VENT GAS FIREPLACE

    Last edited by Tyler Kent; 10-30-2009 at 01:03 PM. Reason: sorry the wrong fireplace model

  8. #8
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Fire stop for gas FP in basement

    From what I can see, they put the firestop in the wrong place, on the bottom of the I-joist with the sides open. If this is true, the firestop is totally useless. Look above the firestop they installed and see if you can see the metal pipe. If you can see the pipe, then it is wrong and you need to get someone who actually has a clue.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Fire stop for gas FP in basement

    Quote Originally Posted by Jim Luttrall View Post
    From what I can see, they put the firestop in the wrong place, on the bottom of the I-joist with the sides open. If this is true, the firestop is totally useless. Look above the firestop they installed and see if you can see the metal pipe. If you can see the pipe, then it is wrong and you need to get someone who actually has a clue.
    Jim,

    That's what I am seeing in there too - they installed that firestop support in the wrong place.

    A couple of more photos from different angles might also help show what was done where.