Thread: Water heater venting
11-12-2009, 06:32 PM #1
I came across this venting set-up for a hot water heater in the basement. House is 20 years old. I immediately remembered the vent at the wall of the basement and thought that this was not acceptable because this is not a high efficiency water heater and should be vented above the roof. I have never seen this type of metal vent(single wall?). I was told by the owner that his contractor from the build did this installation and said it was acceptable. Any help would be appreciated. Thanks in advance.
11-12-2009, 06:36 PM #2
Re: Water heater venting
Oops. Forgot the photos. Here they are. Thanks.
11-12-2009, 06:53 PM #3
It's a direct-vent wtr htr, and it looks like the manufacturers recomendation and instructions, for venting.
11-12-2009, 06:58 PM #4
The vent shouldn't be in contact with the insulation and the paper facing shouldn't be exposed.
11-12-2009, 07:19 PM #5
I have called out the insulation. Is a direct vent water heater that is not high efficiency allowed to vent at ground level? What about gases and exposure to people around them. This is directly under a deck.
11-12-2009, 07:43 PM #6
AO Smith allows it to be under deck a min of 12", and if under the deck is open on at least two sides.
A. O. Smith Water Heaters
scroll down to the promax direct vent pdf
11-13-2009, 06:20 AM #7
This should answer any questions you have. I ran into the same type and found the manual.
11-13-2009, 06:59 AM #8
Thanks again for all your comments and the visuals.