Results 1 to 8 of 8
  1. #1
    Warren Alderman's Avatar
    Warren Alderman Guest

    Default NM liquid Tight to EMT connection

    Last edited by Warren Alderman; 12-20-2007 at 06:55 PM.
    Member Benefits1

  2. #2
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: NM liquid Tight to EMT connection

    Yes as long as they use the correct connector. It looks like they did.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: NM liquid Tight to EMT connection

    Yes, but not like that.

    When done correctly, the liquid tight will come straight down off the fitting at the EMT, not being pulled at an angle at the fitting, as shown in the photo.

    Close ... but no cigar.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    John Steinke's Avatar
    John Steinke Guest

    Default Re: NM liquid Tight to EMT connection

    I'm not convinced that the correct fitting was used. I don't see much of that 'all plastic' stuff, so I don't know if there even IS a single connector for that use.

    Since a section of the stuff is used, the EMT wilol need to have a ground wire in it.

    The application, while it can be done this way 'legally,' is a bit unusual. I'd take that as a clue that some untrained folks were playing with the electric, and look at everything a lot closer.


  5. #5
    dick whitfield's Avatar
    dick whitfield Guest

    Default Re: NM liquid Tight to EMT connection

    It appears that there is an EMT raintite coupling connecting the EMT to the flex. It would be better if they had used an EMT connector, threaded coupling, and a flex connector. A grounding conductor would be needed.


  6. #6
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: NM liquid Tight to EMT connection

    Dick,

    Just as a point of clarification.

    A grounding conductor would be needed.
    Question: If there was a grounding conductor *in* the EMT, then there would not need to be a grounding conductor added. *Assuming* of course, that the ground wire was in the EMT and passed through the liquid tight to the box.

    Or, is the EMT conduit being used as the ground???

    If the EMT was used *as the ground*, then yes, a ground wire is needed. If the EMT has a ground wire in (meaning the EMT was not used as the ground) it and it passes through then no it does not need an additional ground.

    I suppose it all depends on how it is wired, of which, we would never know unless we opened the box.

    That's the question???

    Do we all agree? Or am I missing something here???


  7. #7
    dick whitfield's Avatar
    dick whitfield Guest

    Default Re: NM liquid Tight to EMT connection

    My thought is that you need to run a gounding wire whenever you run non-metallic flex.


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: NM liquid Tight to EMT connection

    Quote Originally Posted by dick whitfield View Post
    My thought is that you need to run a gounding wire whenever you run non-metallic flex.
    Agreed.

    But ... if those are *white* conductors attached to the screws, and if that is a 240 volt circuit, the *white* could be (but should not be) being used as the equipment grounding conductors.

    There "should be" equipment grounding conductor in the non-metallic conduit (any type, flexible or rigid) and those equipment grounding conductors "should be" green (or the "green with one or more yellow stripes except as permitted in this section.").

    If, however, those white conductors are connected to screws which are connected to the enclosure and they are being used as neutral or grounded conductors ... well, that is just plain not allowed and not safe.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com